1794-ADN Flashing I/O LED

rootboy

Lifetime Supporting Member
Join Date
Jan 2004
Location
Tennessee
Posts
1,375
Hi guys,

We have a problem with a 1794-ADN module that is flashing its I/O Status indicator red.

This will flash for awhile and then the Mod/Net will turn red, then it will turn green again (as if it were trying to reset) and then do it all over again.

The original problem appears to be a bad output block in the group. We replaced it.


What we've done so far:

Replaced everything at this point. The ADN, the RTD block, the three output blocks, and the DC input block. And replaced the bases as well.


Any ideas?


Thanks!
 
Sounds like the ADN had 3 out put cards and 1 in put card attached to it.
When you replace the ADN you need to download the IO configuration to ADN. Then it knows what sort of modules are attached to the unit. If you have another ADN with the same IO configuration then you can replace it by just changing the Devicenet address. What is the fault code on the Devicenet Master?
 
Last edited:
Sounds like the ADN had 3 out put cards and 1 in put card attached to it.
When you replace the ADN you need to download the IO configuration to ADN. Then it knows what sort of modules are attached to the unit. If you have another ADN with the same IO configuration then you can replace it by just changing the Devicenet address. What is the fault code on the Devicenet Master?

Sorry about the extremely late reply. We have been buried here.

In the end we changed out the entire stick of I/O using ones we got from an unused machine. That still didn't fix it, so we replaced the DeviceNet scanner as well. That finally got things up and running.


Thanks,

John
 

Similar Topics

I have to configure new 1794-ADN Series C in my devicenet network. I have downloaded the EDS File and registered it. But while configuration in...
Replies
3
Views
1,075
This is killing me. I've only got one facility with DeviceNet and don't really know much about it. We're expanding that facility, and I need to...
Replies
7
Views
2,582
Here is the scenario that I am sorting through. Outputs in a flex I/O rack are commanded on off by a Foxboro DCS system logic via Devicenet to a...
Replies
13
Views
2,604
I have 1794-ADN Flex I/O Adapter connected over device-net network with scanner . The I/O and network status led are blinking RED . I have...
Replies
0
Views
2,338
First of all im using a softlogix 5860 processor connected via 1784 PCIDS card to the 1794 devicenet adapter. my first module is a 16 bit DC...
Replies
3
Views
2,329
Back
Top Bottom