powerflex700 Stop Assertd fault

RodV

Member
Join Date
May 2012
Location
Chillan
Posts
8
Hi there

I have a Powerflex700 connected by devicenet to a control logix system. The drive is commanded by a SCADA but is not working.

In the HIM you can see the drive is in Stop Assertd (parameter 214)

Anybody have an idea of what this can be? Or what parameters should I check?
 
The stop command can come from multiple sources. A command over DeviceNet, a HIM module on the drive, a hardwired circuit to one of the digital inputs on the drive are just a few possibilities.

If you just installed a new drive as a replacement, my money would be on the digital inputs. Off the shelf, they are configured for 3-wire control from the digital inputs. No signal on the stop input = "stop asserted".

If that doesn't help, more info about your system would allow more detailed help.
 

Similar Topics

Hi friends. I am working on PF700, and drive is showing at speed no faults but when I am hooking up the motor, motor doesnt starts and only shows...
Replies
8
Views
1,727
I want to connect my PLC 5/40 to my Powerflex 700 trough RIO remote I/O. I am connected to the PLC trough a 1. How is the wiring in the Remote...
Replies
0
Views
1,276
We have a Power Flex 700 VFD installed which in turn gives power supply to 55 kw motor. Once the VFD tripped due to over heating of vfd. We...
Replies
7
Views
10,116
Hello, I used the powerflex 700 driver,the driver via 20-comm-e with PLC (1769-L32E) communication,I use the rslogix5000 software config the...
Replies
9
Views
2,963
Please help/advice, On Powerflex 700VC with DeviceNet communication card, the drive is off by 15 rpm at 500 RPM, at 100 RPM the actual speed is...
Replies
0
Views
1,262
Back
Top Bottom