Adding 1734 I/O online

mark_f1man

Member
Join Date
Sep 2005
Location
Auckland
Posts
1
Hi, we are doing a project with a ControlLogic PLC and multiple 1734-AENTR adapters.

Is it possible to add an I/O module to the Point I/O chassis when the PLC is online? i.e. can you take the Point I/O chassis offline somehow - add a module - put it back online - all while the PLC is still running. Or is the only way to add an I/O module to take the PLC offline ?

In this case we want to add a 1734-OB4E.
 
Hi Mark,

As a general rule - if it won't let you do something online, then you can't.

In your specific case, no, you can't add any I/O to Logix5000 systems unless they are Logix5000 I/O modules.

You will have to add the I/O modules offline, and do a download to the controller. This, as you most likely know, will stop the controller from working, so be sure to shut everything down to a "safe" state.
 

Similar Topics

Hello. I am struggling with this and it seems it is in from of my eyes but I still don't get it. In Logix 5000 catalog I have registered the...
Replies
12
Views
1,553
Hi everybody, I am having an issue adding a 1734-aent/ series C. My rack is: 1734: Aent IB8 IB8 IB8 field distributor OB8. I get the yellow...
Replies
7
Views
2,666
Hello, Fairly new to PLC programming. Have a question in regards to a 1734 Point I/O rack and the built in tag structure in Logix Designer. I...
Replies
2
Views
2,138
Good Evening , I have a CompactLogix 1769-L18 ,with a 1734-IE4C beside it and I am remotely adding a 1734-AENT, and on the side of that I am...
Replies
5
Views
2,076
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
56
Back
Top Bottom