1734-AENTR installed in Logix catalog, but when adding....

AlfredoQuintero

Lifetime Supporting Member
Join Date
Feb 2015
Location
Yokohama
Posts
1,552
Hello. I am struggling with this and it seems it is in from of my eyes but I still don't get it. In Logix 5000 catalog I have registered the version of 1734-AENTR that I need and is flashed in the actual device. But when I try to add the device to the Logix program the version I see in the installation is different from the version that Logix allows to select.
OK, how can I fix this. The screenshot below should be clearer than my English. Thanks for reading.

1734_Module.jpg
 
I think you need to install the correct AOP in Studio 5000 for that version. You added the EDS file but you also need the AOP for that device before it will show up in Studio.

AENTR AOP.jpg
 
I don’t know if you try to change the series, to see if you can select a different series that can offer a newer revision.
 
@Rob, the version on the AOP download does not represent the version of firmware version it is installing. If you look carefully at the download description, it says that AOP v7.01.02 installs firmware support for series C v6.013. Master class version naming. Edit: You need AOP v8.01.02

capture-20231106-072707.png
 
Last edited:
I really wish they would have went with a different version scheme. Something like v2023.04.15. They are often close enough to the real firmware versions to maximize confusion.
 

Similar Topics

Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
355
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
Replies
16
Views
546
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
Replies
12
Views
536
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
Replies
1
Views
313
Hi there! I've been looking for some fault codes table for the 1734-AENTR adapters, since I'd like to show a message in HMI with some...
Replies
1
Views
584
Back
Top Bottom