1734-AENTR fault codes

mrenton

Member
Join Date
Nov 2023
Location
Madrid
Posts
1
Hi there!



I've been looking for some fault codes table for the 1734-AENTR adapters, since I'd like to show a message in HMI with some information when there is a faulty adapter, but I haven't found anything on the internet.
So my question is, is there any type of table like this for these adapters?
Right now I have a PLC with some AENTR adapters in the program for testing, and since there is actually no adapter connected to it, I can see a 16#2024 error in the module properties, but can't seem to find that info in the module variables.

Do you guys have any clue on how to find this information in order to show it?

Thanks in advance!
 
Welcome to the forum!

You can get the module status with an SSV instruction, directed to the module. Drop an SSV instruction on the rung, select it and press F1, and have a read - the help files have all the information you need.
 

Similar Topics

Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
Replies
1
Views
309
Hello, How can I go about setting up a fault bit if I lose comms to an AENTR module? I have several 1734 AENTR modules on my network. Some...
Replies
2
Views
3,419
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
349
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
Replies
16
Views
536
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
Replies
12
Views
531
Back
Top Bottom