Ethernet_ModbusMaster_TCP issue

Beginer

Member
Join Date
Dec 2012
Location
Singapore
Posts
1
hi,
i am using Ethernet_Modbus_Master_TCP to scan through 10 Wago devices from Wago IPC. Some of Slave devices are not power on but I received "Com OK" status intermittently from those devices. Your advice on how to solve that will be greatly appreciated.


Thank in advance.
 
I don't know a lot about Wago but I have had this issue with other hardware.

What we did was to use a spare output at each station and wire it to a spare input at that same station. Then the Master program flashed the output on and off using a timer. Lastly, the Master program looked for the flashing input at the remote station and if it wasn't present, it considered the station offline.

Hope this helps
 

Similar Topics

Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
203
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
101
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
321
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
Replies
14
Views
479
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
Replies
16
Views
549
Back
Top Bottom