The current application involves a steam jacketed vessel (2000 lbs deadweight), 3 Mettler Toledo load cells (2mV/V), each with a 2500 lb capacity, a summing box and a Panther display.

The Panther display is going to be replaced with a IND110 converter with the 4-20 mA signal reporting to a 12 bit analog card.

The maximum capacity of the vessel is 800 lbs of water.

My normal approach would be to scale the logic so that 4-20 mA equates to 0-7500 lbs (0-4096 counts). Since the active weight spans from 0-800 lbs, this means that only about 10% of the total range is used and the best resolution achieved will be around 2 lbs/count.

The IND110 calibration mode allows the 'zero load' to be set to 4 mA, which would be the vessel deadweight (2000 lbs).
It can then be spanned to set the 'full load' of 2800 lbs to 20 mA.

Now, if I scale the logic so that 4-20 mA equates to 0-800 lbs (0-4096 counts), there will be a much improved resolution.

Is this correct or am I missing something?
 
My normal approach would be to scale the logic so that 4-20 mA equates to 0-7500 lbs (0-4096 counts).
Why is this "normal"?


The IND110 calibration mode allows the 'zero load' to be set to 4 mA, which would be the vessel deadweight (2000 lbs).
It can then be spanned to set the 'full load' of 2800 lbs to 20 mA.

Now, if I scale the logic so that 4-20 mA equates to 0-800 lbs (0-4096 counts), there will be a much improved resolution.

Is this correct or am I missing something?

This is correct, although I would set the full-scale 20mA to higher that 800lbs, say 900, or make it a nice round number, 1,000lbs.
 
I scale pressure transducers to their full range and assumed that I would have to do the same with load cells.

Yes, I am new to load cells and quickly figured out that I could not simulate a 7500 lb load.
 
I scale pressure transducers to their full range and assumed that I would have to do the same with load cells.

Yes, I am new to load cells and quickly figured out that I could not simulate a 7500 lb load.

Unfortunately you will find the steam pressure in the jacket will cause unreliable readings as the ratio of dead weight to live weight is so high. Inrushing steam adds load onto load cells , if the dead weight ratio to live weight ratio is low these fluctuations may not be be noticeable, but in your application where the dead weight is higher than the live weight, steam pressure fluctuations will affect weight readings.
 

Similar Topics

Hey y'all!! I'm looking for an old EDS file, GSE 560. I can't find them anywhere. It is for a GSE560 display on a DeviceNet network, with...
Replies
0
Views
76
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
420
Good Evening , I purchased an Avery Weigh-Tronix - ZM301-SD1 to weigh a tote. The loadcell is a FLS -250. Below is the color code and...
Replies
5
Views
1,289
Can you use the 1756-RIO to read values from a weigh scale with a RS-232 port? I am looking into trying to bring in data from the weigh scale that...
Replies
3
Views
1,459
Typically we interface to dozens of third-party devices that have Ethernet/IP capability WITH appropriate documentation to set up a GENERIC...
Replies
38
Views
28,847
Back
Top Bottom