gphillips
Member
The current application involves a steam jacketed vessel (2000 lbs deadweight), 3 Mettler Toledo load cells (2mV/V), each with a 2500 lb capacity, a summing box and a Panther display.
The Panther display is going to be replaced with a IND110 converter with the 4-20 mA signal reporting to a 12 bit analog card.
The maximum capacity of the vessel is 800 lbs of water.
My normal approach would be to scale the logic so that 4-20 mA equates to 0-7500 lbs (0-4096 counts). Since the active weight spans from 0-800 lbs, this means that only about 10% of the total range is used and the best resolution achieved will be around 2 lbs/count.
The IND110 calibration mode allows the 'zero load' to be set to 4 mA, which would be the vessel deadweight (2000 lbs).
It can then be spanned to set the 'full load' of 2800 lbs to 20 mA.
Now, if I scale the logic so that 4-20 mA equates to 0-800 lbs (0-4096 counts), there will be a much improved resolution.
Is this correct or am I missing something?
The Panther display is going to be replaced with a IND110 converter with the 4-20 mA signal reporting to a 12 bit analog card.
The maximum capacity of the vessel is 800 lbs of water.
My normal approach would be to scale the logic so that 4-20 mA equates to 0-7500 lbs (0-4096 counts). Since the active weight spans from 0-800 lbs, this means that only about 10% of the total range is used and the best resolution achieved will be around 2 lbs/count.
The IND110 calibration mode allows the 'zero load' to be set to 4 mA, which would be the vessel deadweight (2000 lbs).
It can then be spanned to set the 'full load' of 2800 lbs to 20 mA.
Now, if I scale the logic so that 4-20 mA equates to 0-800 lbs (0-4096 counts), there will be a much improved resolution.
Is this correct or am I missing something?