1747-L40C communications

usstrap

Member
Join Date
Apr 2011
Location
South Carolina
Posts
11
Have an old 1747-L40C running process machinery. Over the years, outputs fail, etc and got to the point that I had to replace. Bought a used unit from Ebay but it will not communicate. I have the old laptop with serial port, got the PIC and know it works. Have old copy of the APS software and know it works. This replacement PLC unit shows power but CPU FAULT light is blinking. I cannot get computer to recognize this PLC so can go no further. Can anyone get me on a correct path?
 
The flashing FAULT LED denotes a Major CPU fault, however, this should not restrict the communications capabilities of a functional processor.
Refer to Page 8-6 of http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um009_-en-p.pdf
for probable causes and mitigation solutions.
In order to connect to the CPU and "solve" the FAULT condition, you will need a Serial (RS232) Port PC running RSLogix 500 + RSLinx Lite (or the APC software) and either a 1747-PIC, 1747-KE or a 1747-KF3 adapter in order to connect to the CPU.
Refer to Appendix A of the above posted link in order to setup the CPU comminications.
You might have another shot if you could secure a 1747-DTAM-E hand held programmer; clearing S:1/3, S:5 and S:8 memory addresses might return the CPU to a functional state.
 
Last edited:
I appreciate you responding. I have computer with RXLogix 500 but only USB ports and serial adapter cable. I have the 1747-PIC but trying the 'who active' will not connect.
With my old PC with APS software and the PIC, I had no problem with the identical PLC, it just doesn't recognize that there is anything connected.
 
Let's take a step back: You say you have an old computer, with a serial port and APS software, and a 1747-PIC that is known to work.

But that computer won't browse the "new" 1747-L40C on DH-485.

If this were my system, I would keep trying with that old computer. As Bernie mentioned, you can't use RS-232 converters of any sort with the 1747-PIC. The 1747-UIC is the standard way to connect to DH485 from a modern computer.

If the confirmation the old computer being "known to work" is not very recent, do it again by finding another SLC-5/0x controller to connect with.

The two configuration variations I would try are attempting to use DH485 at 9600 baud, and try node numbers 0, 1, and 2 for the RSLinx driver.
 
I hooked up to the PLC I'm trying to replace and my stuff will connect straight up. I'm asking the Ebay seller if he can exchange this machine with another. Many thanks to you folks for trying to help.
 
The last 1747-L40 that i worked on we replaced it with a ML1200, the only problem was that the inputs and outputs were on the opposite side for each type of processor.
Surely a new ML1100 would be cheaper that an old 1747-L40.
 
You are probably correct but this machine is on a budget and I have to scrape. I have an old 7 slot rack here with I/O cards that will fit this application if processor can be modified in the program. I:O/18 would have to become I:3/2 I think. Can this be done with RSLogix? Old processor 1747-L40C. This one = 1747-L542B. Ladder stuff should function fine.
 
You are probably correct but this machine is on a budget and I have to scrape. I have an old 7 slot rack here with I/O cards that will fit this application if processor can be modified in the program. I:O/18 would have to become I:3/2 I think. Can this be done with RSLogix? Old processor 1747-L40C. This one = 1747-L542B. Ladder stuff should function fine.

Yes, you can change the processor type and then move the I/O.

See here for some tips on that last part:
http://www.plctalk.net/qanda/showthread.php?t=4673
 
I changed the processor and I/O config no problem. The database shows all I/O at both addresses but the ladder display still shows the old base unit addresses and errors re the unconfigured I/O. How do I put this right? I really appreciate your help.
 
Zip the RSLogix 500 .RSS file.
In the bottom of the PLC.net window choose "Go Advanced"; you will be given the option to Attach Files; choose it, point the utility to the recently zipped file ( Browse) and then "Upload" it; "Submit" your Reply.
 
I changed the processor and I/O config no problem. The database shows all I/O at both addresses but the ladder display still shows the old base unit addresses and errors re the unconfigured I/O. How do I put this right? I really appreciate your help.


Brute force. Click on search then use the replace option.
See picture.

I would list all the old addresses and then put next to them the new addresses
and get to it.

searchand replace.png
 
Ok this should be it. I moved the I/O by search/replace; there weren't that many. My next brick wall will be finding the card for this rack that can talk to a OIT that is connected. I really appreciate you guys giving your time.
 

Similar Topics

Hello everybody, I have a slc500 1747-L40C PLC has a similar port of the ethernet port but it is a DH485 port, I want to convert from DH485 to...
Replies
8
Views
1,697
HI guys i have problem with i just receive an old machine with an old SLC 500 1747-L40C but the problem it have is that goes from fault static...
Replies
6
Views
2,243
Dear All, I need to upload program from slc 500 fixed controller (1747-L40C), series "B" and FRN "6"and to download the program to another PLC...
Replies
23
Views
7,259
Just got back from a customer with an L40C (SER C, FRN 6) that immediately faults at powerup. I can download the program, switch to RUN, and it...
Replies
2
Views
1,666
Hello, I have a 1747-L40C processor and 1747-PIC interface convertor, but my laptop system is windows XP sp3,the RSLinx 2.59 version, as I confige...
Replies
6
Views
2,545
Back
Top Bottom