Point IO output modules blinking

bigrthanur

Member
Join Date
Mar 2007
Location
Ohio
Posts
85
Iam using some point IO modules with a 1734-AENT ethernet card. The output modules blink red when nothing is attached. I can shut this off with my RSnetworx for device net under the enable no load or disable no load. but everytime i cycle power it changes back to flashing.

Anyone know what I am missing?
 
Make the change in the RSLogix 5000 module configuration applet, rather than with the RSNetworx Parameter Editor.

Each time the controller establishes an I/O connection to the module, it sends configuration data, which is why it is over-writing your parameter change.
 