hello,
i am working on siemens master 420 drive. using BICO mode drive operate in 3- wire connection (on push button for start and other for stop) but do not work when i use one push button for forward and one to reverse and one for stop . can it is possible to operate the drive in 3-wire connection please help...?:unsure:
 
you need to adjust the parameters
the 440 it is P750 by memory.
there are a number of settingd download the manual from Siemens and adjust accordingly
 
I don´t think this will work. That will be called 4-wire control i think. :ROFLMAO:

You can use the 3-wire control to start/stop, and configure Input3 to change the rotation. Input3 will work outside the 3-wire control configuration. I never tried it but it might work.
 
thanks Nonuke & Iant

but can it is possible to change the rotation when i m using the BICO mode for start/stop...?
please revert back & thanks again.
 
thanks Nonuke & Iant

but can it is possible to change the rotation when i m using the BICO mode for start/stop...?
please revert back & thanks again.

I don't think so. To change the direction, you also need a 2 pos. switch to Din3 (CW / CCW).
CW - when contact is open and CCW when contact is closed.
 

Similar Topics

My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
Replies
4
Views
2,987
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with mm440. all parameters are crosschecked. please help to...
Replies
4
Views
1,570
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0). I'm...
Replies
1
Views
3,069
Hi All I have the SIEMINS micromaster 440 not starting good several times then start after 1 to 2 hours . so I took the AOP kit and opend it >>...
Replies
12
Views
4,468
Dear all, We are working with MM440 at th plant where i'm working. The MM440 is connected to S7 400 PLC. In the hw config the setting is 0PKW...
Replies
2
Views
1,435
Back
Top Bottom