Don isra
Lifetime Supporting Member
hi i need your help
I have a Mitsubishi FX3U plc and screen GOT1000 16 ..
I have two Scales, and two load cells METTLER TOLEDO IND110
I want to automatically fill oil containers.
my load cells are well calibrated, give the correct weight. compare it with a digital scale
but the filling has much error. for example
the weight you should have is 18 Kg but always varies widely
18.2 kg, 18.5 kg, 17.5 kg, 17.4 kg. etc.
I want a more accurate measure and less mistake
and I think the problem is in the control algorithm in the plc
its not fast enough to close the valves in 18 Kg
I can accept an error between 18.05kg and 18.20 kg
a part of code is
[D>= D414 D901]-------------->(M229) valv1
[D>= D416 D427]-------------->(M230) valv2
D414 and D416 are the weight that is filling and D901 and D427 is the weight limit 18.10 kg
when D414 is greater than or equal to D901, M229 is activated and valve should be closed immediately
I have a Mitsubishi FX3U plc and screen GOT1000 16 ..
I have two Scales, and two load cells METTLER TOLEDO IND110
I want to automatically fill oil containers.
my load cells are well calibrated, give the correct weight. compare it with a digital scale
but the filling has much error. for example
the weight you should have is 18 Kg but always varies widely
18.2 kg, 18.5 kg, 17.5 kg, 17.4 kg. etc.
I want a more accurate measure and less mistake
and I think the problem is in the control algorithm in the plc
its not fast enough to close the valves in 18 Kg
I can accept an error between 18.05kg and 18.20 kg
a part of code is
[D>= D414 D901]-------------->(M229) valv1
[D>= D416 D427]-------------->(M230) valv2
D414 and D416 are the weight that is filling and D901 and D427 is the weight limit 18.10 kg
when D414 is greater than or equal to D901, M229 is activated and valve should be closed immediately