calculate flow rate @ 13mA

goodoboy

Member
Join Date
Aug 2010
Location
Houston
Posts
86
I am doing some studying on Flow Measurements and stuck on this problem?

A dp transmitter is calibrated 0 to 80 inH20 and transmits a 4 to 20 mA dc signal. This transmitter is placed across an orifice plate which is sized to create 80 inH20 differential at 6 gpm.

What is the flow rate when the signal is 13 mA dc?

a. 4.5 gpm
b. 3.9 gpm
c. 3.4 gpm
d. 4.9 gpm

I calculate 3.374 gpm, but answer is 4.5 gpm according to book?

Also, what will the signal be if the flow rate is 4 gpm?

Any help please.
 
Last edited:
I came up with the same answer that you did (actually 3.375) so clearly we don't understand the problem!?!

what will the signal be if the flow rate is 4 gpm?

I use that same formula to calculate 11.2 amps.

Thanks all for the help. I am studying the this PE exam and lots work.
 
Last edited:
6 GPM / 16mA (range) = 0.375 per mA
12mA (50%)x 0.375 = 4.5 gpm
But 13 = 4.875 gpm
I would think you may have to look at pressure ans orifice calculations instead
 
The flow rate through an orifice is proportional to the square root of the pressure differential. Flow is not linear! The transmitter is a differential pressure one, so dp is linear with mA. However, you can't forget the 20% (4 mA) zero offset when you calculate the differential pressure.


I use the formula:
Q2 = Q1 x Sqrt(dp2/dp1)


So, at 13 mA 4.5 gpm is the right answer. At 4 gpm you should get 11.11 mA.


Try it again, show your work, and if you can't get it I'll show my work.

 
Last edited:
:site:
The flow rate through an orifice is proportional to the square root of the pressure differential. Flow is not linear! The transmitter is a differential pressure one, so dp is linear with mA. However, you can't forget the 20% (4 mA) zero offset when you calculate the differential pressure.

I use the formula:

Q2 = Q1 x Sqrt(dp2/dp1)

So, 4.5 gpm is the right answer. At 4 gpm you should get 11.11 mA.

Try it again, show your work, and if you can't get it I'll show my work.

At 13 mA
 
I am doing some studying on Flow Measurements and stuck on this problem?

A dp transmitter is calibrated 0 to 80 inH20 and transmits a 4 to 20 mA dc signal. This transmitter is placed across an orifice plate which is sized to create 80 inH20 differential at 6 gpm.

What is the flow rate when the signal is 13 mA dc?

a. 4.5 gpm
b. 3.9 gpm
c. 3.4 gpm
d. 4.9 gpm

I calculate 3.374 gpm, but answer is 4.5 gpm according to book?

Also, what will the signal be if the flow rate is 4 gpm?

Any help please.

The answer is A. Don't forget that Differential Pressure Flow is a Square-Root Function.

4 GPM should be around 11.11 mA.
 
The flow rate through an orifice is proportional to the square root of the pressure differential. Flow is not linear! The transmitter is a differential pressure one, so dp is linear with mA. However, you can't forget the 20% (4 mA) zero offset when you calculate the differential pressure.


I use the formula:
Q2 = Q1 x Sqrt(dp2/dp1)


So, at 13 mA 4.5 gpm is the right answer. At 4 gpm you should get 11.11 mA.


Try it again, show your work, and if you can't get it I'll show my work.


Thanks

what is the specific gravity of water flowing at 60F?
 

Similar Topics

How to calculate flow Rate of water and Steam ton per hour with pressure differential.
Replies
9
Views
32,134
I'm working on an application where I need to calculate the average incoming flow into a wet well cell for the past 30 mins by tracking the rate...
Replies
1
Views
3,356
Hi, I've working in S7-200 project and i need to calculate the flow rate in m3/h by digital input pulses. I've configured the digital input to...
Replies
0
Views
4,346
Hello, I realize this is a PLC forum but thought I would get some good feedback for components by posting this question! We are using corrosive...
Replies
9
Views
8,964
Dear Experts,:) I have E&H flow meter (promag L400 ,5L4C4F, DN450) which has pulse o/p with these specs: Pulse width Adjustable:0.05 to 2000 ms...
Replies
4
Views
2,114
Back
Top Bottom