AECM Member A Join Date Aug 2013 Location Monterrey Posts 4 Sep 6, 2013 #1 Hi, I'm new at PLC programming and my boss just bought a sureservo SVA-2100. We have a AB SLC 500 PLC and I want to know if I can use it to control the servomotor or I must buy a Directlogic PLC?
Hi, I'm new at PLC programming and my boss just bought a sureservo SVA-2100. We have a AB SLC 500 PLC and I want to know if I can use it to control the servomotor or I must buy a Directlogic PLC?
keithkyll Member K Join Date Jul 2005 Location Heath, TX Posts 2,033 Sep 6, 2013 #2 You can use any PLC.
AECM Member OP A Join Date Aug 2013 Location Monterrey Posts 4 Sep 9, 2013 #3 Thanks! Another issue, which communication cable should I use between the drive and the PLC??
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Sep 9, 2013 #4 AECM said: Thanks! Another issue, which communication cable should I use between the drive and the PLC?? Click to expand... What protocol does the drive support? Does your SLC support this protocol?
AECM said: Thanks! Another issue, which communication cable should I use between the drive and the PLC?? Click to expand... What protocol does the drive support? Does your SLC support this protocol?
bernie_carlton Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Yakima, Washington Posts 6,413 Sep 9, 2013 #5 The manual shows Modbus ASCII or RTU - using RS232/422/485 The cable available from AutomationDirect is the SVC-MDCOM-CBL which fits the communication socket on the servo and has stripper/tinned wire ends. Last edited: Sep 9, 2013
The manual shows Modbus ASCII or RTU - using RS232/422/485 The cable available from AutomationDirect is the SVC-MDCOM-CBL which fits the communication socket on the servo and has stripper/tinned wire ends.
AECM Member OP A Join Date Aug 2013 Location Monterrey Posts 4 Sep 9, 2013 #6 I checked it out and found the SVC-MDCOM-CBL too and the SVC-PCCFG-CBL. Can I use either one of them or it must be SVC-MDCOM-CBL?? I don't need the ASD-BM-50A anymore?? http://www.datalibrary.nl/plc/Data/ADC/Specs/sureservolowmed.pdf Last edited: Sep 9, 2013
I checked it out and found the SVC-MDCOM-CBL too and the SVC-PCCFG-CBL. Can I use either one of them or it must be SVC-MDCOM-CBL?? I don't need the ASD-BM-50A anymore?? http://www.datalibrary.nl/plc/Data/ADC/Specs/sureservolowmed.pdf
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Sep 9, 2013 #7 What is the complete catalog number of your SLC? Only the series C Frn 10 or later support modbus protocol.
What is the complete catalog number of your SLC? Only the series C Frn 10 or later support modbus protocol.