Hello all

we replace a module 1734-PDN and the scanner appear a error message
we not see any switch for configure , Do we need to use the RS NETWORK FOR DEVICE-NET for give a module number ?

if so we can upload the module configuration from the scanner and download in to the module

any idea it is a Great Help

4 day Down !!!!

Thank you all
 
The 1734-PDN has no address or configuration. It is a passive device that connects the POINT I/O module data bus to a DeviceNet network.

The POINT I/O modules themselves have node addresses configured in their nonvolatile memory that appear on DeviceNet.

What is the error message that appears on the scanner ?
 
Those numbers must appear when you boot up the scanner; "88" is an LED segment test.

The error code 91 means that the network is in a "bus off" condition.

This very likely means that the blue and white wires are shorted, or the scanner is damaged, or there is some other major physical problem with the network.
 

Similar Topics

Hello all we replace a module 1734-PDN and the scanner appear a error message we not see any switch for configure , Do we need to use the RS...
Replies
0
Views
1,082
Hi, I'm having issues commissioning a new PointI/O module (1734-4IOL) on an existing DeviceNet network (1756-DNB). I am adding the 4IOL module to...
Replies
1
Views
829
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
49
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
16
Views
608
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
231
Back
Top Bottom