1734-IE4C with isolated signals

A_G

Lifetime Supporting Member
Join Date
Jul 2014
Location
MA
Posts
370
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a 1734-IE4C. This is for Non Isolated analog signals according to its manual. i decided to try it anyway. I wired from the "+" device mA to the card, and from the "-" device mA into my 0 VDC common in the electrical control cabinet. This 0 VDC common is not grounded, in case this matters. I do see some values in the PLC around 4.3 mA but I know it should be reading more like 15 mA right now. Can this be because 1734-IE4C is a non isolated input card? Can I make it work somehow? Do I need to buy another card (that is for isolated signals) and if so which one? (I tried googling it but didn't come up with anything, I'm new to Point IO). Thanks in advance!
 
Normally, isolated output means the sensor or converter has an isolated output in other words it contains a form of optocupler so the supply of the sensor is isolated from the output, it means the ouptput needs to be supplied by the analogue input card, i.e. 2 wire wiring where the card supplies the voltage in the 4-20ma loop.
So a non isolated card is fine. not knowing what the device is (I suggest you post tghe make/part number).
In essence the sensor will need a 24v supply the analohue card then needs to be active i.e. you supply 24v from the card (or other source) in a 2 wire configuration In the case of the analogue card the supply for the 4-20ma signal is sourced from the cards internal bus i.e. 4 wire configuration as in this manual for 4 wire connection
 
Measure with an V-meter directly on the input + and - leads to the device. Do you have the required 24V ?
Measure with an mA-meter directly on the output + and - leads from the device. Do you get the expected 15 mA ?

An isolated transmitter can work with a non-isolated PLC input.
You just have to figure out the path for the current signal to and from the transmitter.

This 0 VDC common is not grounded, in case this matters
If the 0 VDC is the same used for the transmitter and the PLC it should be OK.
 
Normally, isolated output means the sensor or converter has an isolated output in other words it contains a form of optocupler so the supply of the sensor is isolated from the output, it means the ouptput needs to be supplied by the analogue input card, i.e. 2 wire wiring where the card supplies the voltage in the 4-20ma loop.
Good to know, I always thought that "isolated" just means "separate common" and "non isolated" means "shared common".

In essence the sensor will need a 24v supply the analohue card then needs to be active i.e. you supply 24v from the card (or other source) in a 2 wire configuration In the case of the analogue card the supply for the 4-20ma signal is sourced from the cards internal bus i.e. 4 wire configuration as in this manual for 4 wire connection
The device is a "Prismatic Trace Gas Analyzer" instrument, attached is a screenshot of the user manual where it shows how to wire the device connector. I do not see where the +24 VDC supply is supposed to go. I will ask the vendor if I need to wire +24v to the device and if so then where.

Measure with an V-meter directly on the input + and - leads to the device. Do you have the required 24V ?
Measure with an mA-meter directly on the output + and - leads from the device. Do you get the expected 15 mA ?
I will try this

Thank you both!
 

Attachments

  • scrn10.jpg
    scrn10.jpg
    66 KB · Views: 5

Similar Topics

I am running out of real estate in my panel. I have several IE2C cards. I would like to convert them over to IE4C to create space. Rockwell...
Replies
1
Views
1,350
Just wondering if it is possible to wire in a Cynergy UF08B100 Flowmeter into an Allen Bradley 1734-IE4C. I have tried every way I can think of...
Replies
13
Views
3,235
Hi everyone, As stated in the title, this is my first time configuring a 4-20mA device and I am using Rockwell's 1734-IE4C module as part of the...
Replies
20
Views
6,452
Good Evening , I have a CompactLogix 1769-L18 ,with a 1734-IE4C beside it and I am remotely adding a 1734-AENT, and on the side of that I am...
Replies
5
Views
2,083
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
66
Back
Top Bottom