Since I've never had more than 6 in parallel, I won't argue Dick's advice. Mine have been 25% or so over the total FLA.
I will advise, since it hasn't been mentioned, that each motor needs overload protection.
If you use overload relays, you can wire the n/c contacts in series, and then program one of the inputs of the drive for a N/C fault input. This will stop the drive if any 1 motor faults.
In some applications, such as fans, folks use Manual Motor Starters (Motor Circuit Protectors, etc.), which will disconnect the motor which is overloaded. Caution with this one, due to the high voltage spike when disconnecting a running motor.
If the total of the motor leads are longer than 200' or so, or the motors might be disconnected while running (like with the MCP above), use an output reactor from the drive to the overload devices.
Try not to design a system where the motors are switched on with a running drive (line starting) PLEASE! The 6-12xFLA doesn't do anyone or anything any good!