Rahma,
I see
here that you've received some help from the Siemens Technical Forum. Ste39 linked you to the
SIMATIC S7-1200 Programmable Controller System Manual for an example wiring diagram for your relay outputs. If you also look at the
Digital inputs and outputs section, specifically
Digital Outputs, you'll see the permissible voltage ranges and current rating for the CPU 1211c relay outputs:
Voltage range 5 to 30 VDC or 5 to 250 VAC
Current (max.) 2.0 A
rk155 said:
...Please guide me which AC contactor (model of the contactor) will be okay to be used here?...
We are only advising you as to the possible voltage and current you can switch to a contactor
coil with these particular relay outputs. It would be very difficult to specify an exact contactor model without knowing what the contactor itself is switching.
rk155 said:
...I wish to connect a AC contactor with the output since I am dealing with high power dissipation...
Are you referring to AC for the coil voltage, or for the voltage the contactor needs to switch?
If the latter, are you referring to "
high power dissipation" as a high make/break arc current on the contactor's contacts as a result of an AC load?
If so, this has no bearing on which coil voltage you select, but does have a bearing on which contactor model is selected.
While it's important to use surge suppression across the coil, this only helps to protect the PLC relay contact from degradation. The coil voltage has nothing to do with arc suppression across the contactor's contacts.
Depending on the manufacturer you use, a coil surge suppressor is often available. You may also have a preference for a particular contactor manufacturer?
You are attempting to select a power contactor from the control side of things. It's more important to select a contactor to suit your application's switching load, duty cycle and fault withstand current. Then select the coil voltage to suit your control circuit. Most contactors can be ordered with different coil voltages, so this should come last.
G.