Hi Folks I am configuring an OLDI card that requires me to create a message instruction in the PLC to trigger an event in the card. I create a new Controller tag of the type MESSAGE but when I do a verify, I get a warning "message tag not configured" When I try to use the tag in thre message Control block I get an error that no tag has been specified. I am running RSLogix5000 V20.01 Any help please!
Cheers S
 
The message instruction itself needs a tag name defining and whatever data you are reading or writing to and from in your message instruction also need separate tag names defining. I may be misunderstanding what you are saying but I read it as though you were trying to use the tag name for the message instruction within the configuration options for the message control block.
 
body { font: 12px/1.3 "Helvetica Neue",Helvetica,Arial,sans-serif; color: #333333; line-height: 1.6; }a { color: #aaaaaa; }.messageBody blockquote { border-left: 1px solid #CCCCCC; margin-left: 10px; padding-left: 4px; }.badimagesdisabled { background: url('/images/blocked_image.png') no-repeat scroll center center transparent; cursor:pointer; min-height: 40px; min-width: 40px; border: 1px #E3E3E3 solid; }* .badimagesdisabled { height: expression( this.scrollHeight < 41 ? '40px' : 'auto' ); width: expression( this.scrollWidth < 41 ? '40px' : 'auto' ); }.highlight { background-color: #B5D5FF; }#bodyWrapper { .overflow-x: scroll }
v\:* {behavior:url(#default#VML);} o\:* {behavior:url(#default#VML);} w\:* {behavior:url(#default#VML);} .shape {behavior:url(#default#VML);}


This is the information that I have been given to create the message, this was the email sent to me by the suppliet of the card.

Start of Email:



and here’s an example of MSG instruction in the ControlLogix:





image006.png






image007.png






To create a Message Instruction that can cause a tManager Event trigger to fire…


1. Use the RSLOGIX5000 Tag Editor to create a tag at controller scope with a MESSAGE data type.


2. Go to the Ladder Editor, and insert a rung that contains a MSG. instruction. The instruction operand


should be the MESSAGE tag you just created.


3. Click the button to the right of the operand to go to the Message Configuration dialog.


4. For Message Type, choose "CIP Generic".


5. For Service Type, choose “Set Attribute Single” (which has a Service Code of 10), and you will be able


to manually enter the Class and Attribute to which the service is to be sent.


6. For Class, enter 4.


7. For Attribute, enter 3h.


8. Leave Source Element blank.


9. For Source Length, enter 0.


10. The Instance (decimal) must match the Message Instance specified in the associated tManager Event


trigger. Valid values are 1024 thru 4095.


11. Click the Communication tab.


12. For Path, enter module name or CIP path to the module.


13. For Communication Method, choose "CIP".


14. Check "Connected".


15. "Cache Connections" may be checked or unchecked. A check is recommended for in-rack Messages


that occur more often than 1/sec, or for ‘remote’ PLC Messages that occur more often than 1/5 sec.





If a MSG instruction fails due to a connection related problem (data size mismatch, config parameter


mismatch, etc), one of the AB pre-defined error codes will be used (as defined in RSLogix5000 help). If


the fired trigger fails due to a tManager processing error (trigger disabled, mapped tag I/O error, etc),


the base error code is set to generic (FFh) and the extended error code is set as follows:


7001h = General (internal) error


7002h = Invalid mode for request (module halted)


7003h = Trigger already in process


7004h = var/ref/tol I/O or compare overflow error


7005h = Trigger disabled or var/ref/tol condition == FALSE


7006h = Trigger failed (probably tag I/O error)


The MSG done bit is not set until the trigger completes (successful or not).





Let me know if you can get it to work.





If you do not need to use a message instruction to fire the transaction, you can use a PERIODIC trigger, and periodically monitor a tag in the PLC.


This type of trigger doesn’t require any ladder logic in the PLC.

End of Email:





 

Similar Topics

Where is the information for RSLogix Message Control tags stored. Some of the information is accessable but some is not. I recently developed a...
Replies
2
Views
4,388
Hello, I have a question on an OCR application I am doing. I am reading in 16 characters that come from a camera into the plc in its input words...
Replies
4
Views
1,276
I want to read several disparate values of different data types from a second PLC with the MSG instruction via CIP Data Table Read message type...
Replies
11
Views
5,024
Hi, right now I have a real PLC on which i'm connected by ethernet right now, and i'd like to simulate a second PLC with RSEmulate and make...
Replies
2
Views
1,531
Hi, guys, how’s going? If we want to configure a Logix5000 Message, then send it from controller AA to controller BB, should we add controller AA...
Replies
3
Views
1,507
Back
Top Bottom