Hi, guys, how’s going?

If we want to configure a Logix5000 Message, then send it from controller AA to controller BB, should we add controller AA on controller BB I/O Configuration? Or we just need to set up the communication path properly (attachment 2)?

Because as attachment 1, in CUT project, we can read the message which comes from controller RAIL properly, even there is an exclamation point (!) on controller RAIL in CUT project I/O Configuration.

Thanks a lot.

1.JPG 2.JPG
 
With MSG instruction, you do not have to configure the other PLC in your IO Tree.

However, doing it would make your path statement easier to configure because you can just point your path statement to the name of the PLC you configured in your IO tree. Clear as mud?
 
You do not need to have the Target controller in the I/O tree of the Originator controller to send a MSG instruction using a ControlLogix or CompactLogix controller.

I agree that it makes it easier to select the CIP Path string. But it is not required.

In the screenshot you posted, the I/O tree is incomplete for this purpose; it shows only the 1756-ENBT Ethernet module (WUPPER_RAIL) but not the ControlLogix CPU itself on the backplane.
 

Similar Topics

Hi folks. I have a system that I'm working on that needs 2 alarms banners with different event subscription: - One banner for a specific area...
Replies
6
Views
149
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
174
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
251
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
Replies
0
Views
170
Hi all, the machine I am programming the Rockwell PLC for has about 100 parameters that need to be adjusted for every customer. I would like to...
Replies
20
Views
2,022
Back
Top Bottom