Msr124rt
unsaint32 said:
In this relay, what is the differnce between X1/X2 loop and Y1/Y2 loop? Both have to be closed to energize K1 & K2, right?
Not to cut across you Ian, but I thought I'd explain these terminals in a little more detail...
The X1/X2 loop is technically known as the "Monitoring Feedback Loop", but is more commonly referred to as a "Monitored Output Loop". It verifies that devices wired to the Safety Outputs have de-energized correctly. As you can see they are wired in series through Normally Closed auxiliary contacts on the Safety Contactors K1 and K2. When the Safety Contactors are de-energized, the X1/X2 loop is closed. This closed loop is one of the prerequisites to Resetting the Safety Function i.e. the Monitored Safety Relay (MSR). It is optional. If you are not using Monitored Output, then you can loop out X1 and X2.
Y1 and Y2 are as Ian mentioned, the Reset terminals. The MSR124RT has a couple of Reset methods...
Automatic Reset: Here there is no Manual Reset push-button. You loop out the Automatic Reset terminals X5 and X6. Monitored Output is still optional. So if X1/X2 are looped out (No Monitored Output), and Automatic Reset X5/X6 is also looped out, and the Safety Channel Inputs from a light-curtain, gate, or E-Stop are closed, then the Safety Relay will automatically reset.
Some people gasp at this! Surely not? But it is permitted to Auto-Reset a Safety Function immediately upon the closure of the Safety Channel Inputs, under certain cirmcumstances. As always, a Risk Assessment will determine if it is permitted or not.
Manual/Not Monitored: As it states, the X1/X2 Monitoring Output loop is not used, so again, X1/X2 are looped out. Here a Manual Reset push-button is used, and is wired across Y1/Y2. Once the Safety Input Channels are closed, then the Manual Reset can be actuated.
Manual/Monitored Reset: This is a Monitored
Reset, not to be confused with the Monitored
Output feature. Again, a Manual Reset push-button is used across Y1/Y2. Monitored Output (X1/X2) is still optional here. When the Safety Channel Inputs are closed, this MSR incorporates a 5 second delay before you can Reset the Monitored Safety Relay. After 5 seconds has elapsed, a Leading Edge from the actuation of the Manual Reset push-button is required to Reset the MSR.
unsaint32 said:
Before the sequence number 3, if X1/X2 loop was open (meaning the NC contacts did not close, or X1 & X2 were not wired at all), would K1 & K2 still energize?
Hopefully the above makes it more obvious, but if not...
The MSR will never Reset, using any method, if the Monitored Output loop X1/X2 is not closed. As I said, if you do not require it, you can loop it out.
Regards,
George