Panel builder error (4092)

John Phillips

Member
Join Date
Jun 2004
Posts
1
Hello, can anyone help as I am new to AB plc's and panelviews. I have panelbuilder 32 version 03.80.00 and a panelview 550 2711-K5A5 ser F FRN 3.14 which I can upload from, modify the program and download to but if I open a new application, write the software and try to download to the panelview the error (4092)-application file is an incompatible firware version appears. I have tried several times but with the same outcome. Am I over looking something obvious or just plain stupid???? Any advice will be gratefully received, thanks John.
 
Catalog & Revision numbers

When you start a new application there is a button that says "Catalog & Revision Numbers". Press this buuton and then you can pick the firmware that your PanelView uses.
 
John,
When you upload the file, the terminal configuration is also recovered. Check this against what you are trying to download. The target device or type should be the same. You may be dealing with a firmware version error, check your developement software compatability with the firmware on the PV device. If you uploaded the file with a newer revision that is upward compatable it will most likely not be able to re-download to the device until it is also at the same revision level.

Bitmore
 
Last edited:
Sorry to revive such an old thread....

But I did a google on this error, and this thread came up. While the information contained was helpful, I just wanted to add a couple things in case someone ran across the same problem I had.

As Bitmore stated this was my problem, but I was looking to solve it in the wrong place.


To look in the correct place, do the following:
  • Open the project tree on the left side of the PanelBuilder 32 screen.
  • Expand Application settings.
  • Click on Terminal Setup.
  • Then look right under the Terminal name where it says selected Terminal. This info (both catalog # and firmware revision) should match the terminal you are going to download to.
  • If it does not match, click on the Catalog and Revisions button near the bottom and then select the matching Panelview.
  • After you click OK, the software will update the program so that when you now try to download all will be well.
 

Similar Topics

I did a few searches looking for info on this subject and couldn't find anything. Sorry, if this is an old topic. I am new, not just to this site...
Replies
7
Views
2,367
Hi, we are using PV300 and using Panel Builder 32 as software. We are receiving the error code as 31. Please let us know how to clear this error.
Replies
3
Views
7,938
I recently installed Panel Builder 32 v3.83.01 onto a laptop running Windows 2000 SP2. Everything worked fine. I edited the PB32 application, and...
Replies
3
Views
5,807
I am adding to a current application and keep getting error code 9077 when i try to validate the changes I have made. I added a maintained push...
Replies
4
Views
2,941
Does anyone know where I could download panel builder 32 for old rockwell HMI's? Our supplier is no help and we are struggling to find the...
Replies
2
Views
900