Micro850 with Analog Outputs Module - No Output Signal!

PhilPike

Member
Join Date
Oct 2014
Location
Montreal
Posts
8
Greetings,

My company is working on a panel for an OEM and it is the first time we are using the Micro800 family - specifically the Micro850 with one Analog Input module and one Analog Output module.

The panel is built and we are trying to test everything and for some reason we can't get the analog outputs to output anything.

Has anyone seen this before or have any suggestions?

Thanks,
Phil
 
Thanks for the response.

Yes - it has been configured to 4-20mA in CCW and it is wired accordingly.

So even without simulating any actual values, the minimum should be at 4mA but we are reading 0.
 
It sounds like you might not have power connected to your OF4 COMMON trminals. Without power, you will get 0 Output values.
 
Commons are wired OK.

Called AB and .. turns out that if the analog outputs detect an 'open wire', like what you would get if you tried to measure them (closing the loop) and then removing the multimeter leads (opening the loop once more), the PLC generates a fault and that fault needs to be cleared before any other output signals can be sent.

Seems like a very strange way to do it to me. Not to mention this particularity is not very well documented.

Like many others, we have had a mostly-negative first experience with these Micro800 series controllers.
 
Like many others, we have had a mostly-negative first experience with these Micro800 series controllers.
Thanks for the heads-up. This type of experience is priceless information for someone making a decision about which PLC to buy.
 
I've had a similar problem with an 2085-OF4 module today working on a job site. The module would not output 4-20mA despite checking and rechecking the settings. Out of frustration, I tried resetting the module to output 0-10V, and it seemed to work.

Is this problem, where you have to reset the module to get a valid output, still a problem on recent 2085-OF4 modules?
 

Similar Topics

Hello, As you may remember, I posted in January about an issue we were having with our micro850 controllers (2080-LC50-48AWB) to operate...
Replies
16
Views
4,304
Hello, We are using 80 micro850 controllers (2080-LC50-48AWB) to operate irrigation booms in our nursery. We are using an analog output card...
Replies
15
Views
7,297
So I'm running a liquid filling operation and I'm trying to get the dribble valve to be open 100% for a time and then 20% for the rest. all that...
Replies
6
Views
2,262
Hello, I have a question regarding the analog output modules on a AB Micro850. I'm not getting an output to my valve and when I put a meter on it...
Replies
2
Views
1,544
Having some trouble with getting data from this expansion module: I'm not sure what I'm missing here. No matter how many volts are being put...
Replies
7
Views
3,274
Back
Top Bottom