I have eight remotely-mounted thermistors that are part of an air handling unit (two units, actually). We have replaced the old Delta Control units with a PLC that we can program & troubleshoot in-house. Outside air and room temperature sensors are RTD type, but I just realized that sensors internal to the AHUs are thermistors.

I know I can use a universal signal conditioner to change the thermistor "signal" to a 0-10V or 4-20 signal, but I would need eight of them.

I'm hoping someone knows of a multi-channel thermistor input device capable of modbus communication.

Also, I've had good results in a previous project where I used one available 0-10V input point to connect to several RTDs using an eight-point relay output card. I'm wondering if, perhaps, I could do the same sort of thing with a single signal conditioner. The original project didn't require rapid response, so I would cascade through the relay outputs, one at a time, holding each closed for 10 seconds. All output COM were connected together and were connected to the universal signal conditioner. The last reading was considered "good" and was maintained until the next cycle, 60 seconds later.
 
I have eight remotely-mounted thermistors that are part of an air handling unit (two units, actually). We have replaced the old Delta Control units with a PLC that we can program & troubleshoot in-house. Outside air and room temperature sensors are RTD type, but I just realized that sensors internal to the AHUs are thermistors.

I know I can use a universal signal conditioner to change the thermistor "signal" to a 0-10V or 4-20 signal, but I would need eight of them.

I'm hoping someone knows of a multi-channel thermistor input device capable of modbus communication.

Also, I've had good results in a previous project where I used one available 0-10V input point to connect to several RTDs using an eight-point relay output card. I'm wondering if, perhaps, I could do the same sort of thing with a single signal conditioner. The original project didn't require rapid response, so I would cascade through the relay outputs, one at a time, holding each closed for 10 seconds. All output COM were connected together and were connected to the universal signal conditioner. The last reading was considered "good" and was maintained until the next cycle, 60 seconds later.

AB's Micro 820 says it will support 4 thermistor inputs on the embedded IO. Not sure about linearity or resolution though.

They cost about $200.

http://ab.rockwellautomation.com/Programmable-Controllers/Micro820
 
You can even control them with your plc, or via 4 relais or with some resistors direct making 5 volt from the 24 volt. (i would use some optocouplers.
and yes it is only one simple IC, placed on a small PCB.
you can take a look at arduino, also for the rest of the controls, you will be surprised by price and possibilities.
you can use a XTR105 to make the RTD or NTC, PTC signal 4-20 mA.
power supply of the board can be a simple 24 volt connected to a 7805.
 

Similar Topics

I have TM221CE40R controller along with TM3TI8 temperature module. Temperature sensor we are using is Thermistor with below part no. AXIO...
Replies
2
Views
1,971
L
i would like to know is it possible to connect and make a thermistor to give a signal to PLC.....PLS let me know as soon as possible....
Replies
10
Views
8,691
I have a motor with 2 thermistors. One pair reads 1.0 ohm and the other 247 ohms Does this indicate one of them is bad? Which one? Also these...
Replies
4
Views
1,641
Can someone explain how a Powerflex 525 drive interprets the PTC Thermistor signal from a motor winding? How does one know what the levels are or...
Replies
3
Views
4,023
Thermistors........Can someone explain how they work and how to control the speed of a vfd with them? I am not familiar with thermistors, but a...
Replies
31
Views
5,930
Back
Top Bottom