vfd speed controlled by a thermistor
Does the drive have PID capability?
For a cooling tower application, shouldn't you be using the water temperature as the feedback? You would also like to monitor/calculate the outdoor air wetbulb temperature to bound your setpoint.
A cooling tower can be used to cool the water to perhaps 5-7degrees higher than ambient wetbulb temperature, but not lower. SO if the ambient wetbulb is 78F, you should be able to cool the water to ~83F. If the wetbulb is 85F, you will not be able to cool the water to 85F no matter how hard the fans run.
The vfd does have PID capability.
I am not the engineer on this job and I am not familiar with all the details on cooling towers. I am basically making sure they have the hardware to do what they want to do.
But thanks for your suggestions. I may be able to suggest improvements to them along the way.
Also. This motor is only a 3hp so I believe it is some auxiliary motor and not used for the main cooling action
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
160
Working on 2 VFDs for two motors, they follow any speed command when local and in hand. Once I try to give a Speed reference from my PLC they both...
2,206
Hello, So I was asked to turn up the speed on a VFD to allow a carriage to move a little bit faster and avoid getting stuck. Im not sure the exact...
742
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
2,634
I don't understand how vfd detects speed when we are running in open loop control (sensorless). For me only possible way; during auto tuning it...
2,666