Hi I have a closed vessel of product (mostly water) and the level is controlled by differential pressure

If the max vessel pressure is 4 bar is this correct

Scale both transmitters to 4-20mA = 0-4 Bar

Level =Bottom Pressure - Top Pressure

Or is it more complicated than that
 
How big is this vessel?

If 4 bar is the pressure in the vessel and not the actual level then you need a differential
transmitter that will handle the pressure but it is not the range for measuring the level.

https://www.google.com/?gws_rd=ssl#q=one+inch+of+water+column+in+psi

Typically this is done by one differential transmitter, high side connected to the bottom and low side piped to somewhere above the level.
 
Last edited:
It sounds like you're proposing to use two gauge pressure transmitters, one at the top to measure the vapor pressure, the other at the bottom which sees the liquid level head pressure AND the vapor pressure and then subtract both readings to get level.

Yes, it can be done, but with an expected error that will be much higher than if you use a DP transmitter with two ports, a high and a low side.

A level measurement of say, 4 meters water column (wc) of liquid level, is a maximum head pressure of only ~0.4 bar. But you need two transmitters capable of static pressure 4 bar range (~40m wc head pressure) because of the static pressure of the closed vessel. The entire span of the level (0.4m wc) is probably only 1/10 of the range (40m wc) of the transmitters you're using.

The range of a DP fits the level measurement because its range is the subtracted value range, not the static pressure range. A DP does internally what you propose to do with two individual gauge pressure transmitters, but it does so without the combined error of two separate transmitters that are both ranged to be able to read the static pressure.

A DP compensates for the common static pressure by its internal design, so that its range more closely matches the level span, not the static pressure span.
 

Similar Topics

I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
Replies
17
Views
4,481
Any recommendations for a DIY home automation suppler that has a inexpensive WiFi device that I can use to monitor my HVAC filter. Thanks, Bob O.
Replies
13
Views
3,358
On site we have Yokogawa EJA110E differential pressure transmitter connected to process air line. I'm not sure if this can be used to measure air...
Replies
9
Views
4,474
Hi, I am working on a current system using a Bailey Differential Pressure Transmitter. Unfortunately the label is torn off, the only thing left...
Replies
2
Views
1,725
Has anyone used a sensor like this on flammable gasses like natural gas? I have an orifice plate installed in a gas line that I'd like to...
Replies
17
Views
7,132
Back
Top Bottom