The Mixer came from China with a S7-200CN, 224XP CPU.
3 Chinese VFDs. V&T E5-H. Wired together with RS485, 2 wire.
9600, no parity. 3 different sizes. I think 20-50 HP. 480 service at 400 Amps.
The PLC was changed to S7-1200, 1215C CPU and RS485 serial comms module. CM1241, the big one that attaches to the right of the CPU.
Runs most of the time, but overnight it will lockup.
I suspect noise on the RS485 communications. No LED's flashing for communications. 24DC Power cycle restores comms.
I can detect fault in software. Modbus reports code 8200 for all VFDs.
Is there a way to do a soft reset of the RS485 module with code?
I put two counters on it to count faults with read and write.
Overnight, writes were 285, reads were over 3000. This is with the VFD's idle.
I'm going to rewire with shielded, and check for a terminating resistor. Even so, I don't want another lockup. The S7-200 didn't - what did I do wrong?
3 Chinese VFDs. V&T E5-H. Wired together with RS485, 2 wire.
9600, no parity. 3 different sizes. I think 20-50 HP. 480 service at 400 Amps.
The PLC was changed to S7-1200, 1215C CPU and RS485 serial comms module. CM1241, the big one that attaches to the right of the CPU.
Runs most of the time, but overnight it will lockup.
I suspect noise on the RS485 communications. No LED's flashing for communications. 24DC Power cycle restores comms.
I can detect fault in software. Modbus reports code 8200 for all VFDs.
Is there a way to do a soft reset of the RS485 module with code?
I put two counters on it to count faults with read and write.
Overnight, writes were 285, reads were over 3000. This is with the VFD's idle.
I'm going to rewire with shielded, and check for a terminating resistor. Even so, I don't want another lockup. The S7-200 didn't - what did I do wrong?