Powerflex4 /40

PLC Pie Guy

Member
Join Date
Jun 2013
Location
Halifax
Posts
1,144
Hey all.
I just wanted to ask a quick drive question.
I am trying to commision an old panel that came from another plant. It has many sets of drives all powerflex4, communicating through 22X Comm modules. Each 22X Comm module carries 5 drives and is communicating to the CLX through ethernet.
My question is this. I have one failed drive. I only have a powerflex 40 to replace it with at the moment. If I address the powerflex 40 with the same node or module address, would this be a suitable direct replacement? I am thinking that maybe the method of communication would be different to the PLC than the powerflex 4 was.
Any input will be appreciated.

Thanks
 
Make sure the baud rate and the format are the same as the PF4. I think it will work as long as only the basic information is being accessed (status/actual freq in - command bits/commanded freq out)
 
I agree; I don't think that the 22-COMM-E module does any identity checking at all on the DSI serial side.

You'll have to set the DSI node number correctly, and of course set up any non-default parameters and current limits, etc.

But the Start/Stop command and the speed reference scaling are all identical in the PowerFlex 4/40/400 series, as far as I know.
 
Thanks for the input guys. I thought it should work because looking at the manual the parameters are the same and I am only communicating basic start, stop, running at speed and such. However I figured something I was totally overlooking would keep me from making this work.
I am going to try this later today.

Thanks again!
 

Similar Topics

Quick question on the Powereflex 4 probably pertains to most drives. Does setting the stop command to "coast" eliminate the deceleration setting...
Replies
5
Views
1,707
Getting back into this after a few years, was drewcrew6 back then. Can the pv talk directly to the powerflex, ability to start stop jog drive...
Replies
4
Views
2,298
I'm new to the forum and have limited knowledge of PLCs and FReqDrives. I'm the only maint man where I work and need some info please. I have a...
Replies
17
Views
4,992
Hi, I need to do Modbus communication between PLC(L73S Controller) and Powerflex 4 Drives. Does anyone tried this before? Thanks, Vinod
Replies
1
Views
1,462
We have a powerflex4 drive I am going to over speed or overclock take from 60hz to a 100hz Any reasons you would suggest not doing this I just...
Replies
4
Views
2,189
Back
Top Bottom