Powerflex4 /40
PLC Pie Guy
Jun 2013
Halifax
1,144
Hey all.
I just wanted to ask a quick drive question.
I am trying to commision an old panel that came from another plant. It has many sets of drives all powerflex4, communicating through 22X Comm modules. Each 22X Comm module carries 5 drives and is communicating to the CLX through ethernet.
My question is this. I have one failed drive. I only have a powerflex 40 to replace it with at the moment. If I address the powerflex 40 with the same node or module address, would this be a suitable direct replacement? I am thinking that maybe the method of communication would be different to the PLC than the powerflex 4 was.
Any input will be appreciated.
Make sure the baud rate and the format are the same as the PF4. I think it will work as long as only the basic information is being accessed (status/actual freq in - command bits/commanded freq out)
I agree; I don't think that the 22-COMM-E module does any identity checking at all on the DSI serial side.
You'll have to set the DSI node number correctly, and of course set up any non-default parameters and current limits, etc.
But the Start/Stop command and the speed reference scaling are all identical in the PowerFlex 4/40/400 series, as far as I know.
Thanks for the input guys. I thought it should work because looking at the manual the parameters are the same and I am only communicating basic start, stop, running at speed and such. However I figured something I was totally overlooking would keep me from making this work.
I am going to try this later today.
Thanks again!
Quick question on the Powereflex 4 probably pertains to most drives. Does setting the stop command to "coast" eliminate the deceleration setting...
1,708
Getting back into this after a few years, was drewcrew6 back then. Can the pv talk directly to the powerflex, ability to start stop jog drive...
2,301
I'm new to the forum and have limited knowledge of PLCs and FReqDrives. I'm the only maint man where I work and need some info please. I have a...
17
4,994
Hi, I need to do Modbus communication between PLC(L73S Controller) and Powerflex 4 Drives. Does anyone tried this before? Thanks, Vinod
1,463
We have a powerflex4 drive I am going to over speed or overclock take from 60hz to a 100hz Any reasons you would suggest not doing this I just...
2,191