Why do I have 120VAC from ground to a Triac output that is not on ???

Triac outputs leak. Try putting a pilot light on the output for a check to see if the output is actually on.

Are you trying to provide an E-Stop signal to the down stream machine? Best to keep those in a "hard wired" (i.e. relays and pushbuttons) circuit and not rely on the PLC for that.

If it is a simple control signal it still may be easier to use an interface relay to avoid problems if the PLC's are powered at different potentials.

nOrM
 
yeah, but

Also, it may not matter if the output is on or not as there will be leakage through the triac. Should also point out that in failure mode a triac will almost always fail in a shorted condition, so there would be voltage present all the time. I would completely remove power from all terminals and check resistance across the output side against a known good one, if available and compare results. A zero ohms reading should indicate a failed triac.

Bob
 
You can parallel a 10k ohm resistor with the output eliminate the false reading caused by the leakage of the triac.

10k.jpg


no10k.jpg






If you have a 'wiggins' or other solenoid type voltage checking device they will read 0 if the triac is not gated.
 
you need a wiggy or a voltprobe with a low resistance button

any solid state device leaks. if you are using a multimeter, forget it, as it will show 110V across a digital 110V output card, with the output off without a load. I always use a Voltprobe, which has a button you can push to put a load in the circuit, which will show you the true value which is probably 0V. You would not be the first person to chase their tail due to leakage. I would be included in my early years.
Bob
 
I'm not sure if this is your problem, but you can also get a false reading if you lose a common neutral. A few years ago we had an output card showing one side of a solenoid valve was on, but the valve stayed in the center position. There was 120V on the terminal, the coil's resistance read good, the fuse was good, but when I checked the voltage on the other coil, it also read 120V. I changed the output card and got the same reading. After several hours, I finally clipped a jumper from the common neutral of the two coils to ground and the valve moved and the mysterious voltage on the other coil went away. Turns out the neutral wire in a flexible conduit some how got pinched in half.
 
Not every one is an expert, big fella

Thats for sure.

Tboatman,

Did not mean to come across that way. Some time the guys that are new to this career have to learn to exhaust their efforts trying to read/research everything available.

This "effort" will be a very important part of any job you encounter.

Any device you want to learn, grab a test bench and some modules and go for it! :D (Damn,thats 2 smiles today.)
 

Similar Topics

Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
Replies
3
Views
365
Hello all, I have a relay timer connected to an Allen Bradley 1756-OA16I output card. The output was on, but instead of getting 120VAC we only...
Replies
3
Views
827
the age old question / issue a friend has bought a 1000watt 120vac 60hz rated appliance from the USA into Australia (which has a 240Vac 50Hz...
Replies
10
Views
2,446
by spec i must supply surge protection for each individual PLC input in my panel. These devices are all of the voltage free (dry contact type)...
Replies
11
Views
2,244
Good afternoon, I have an application where we induction harden different areas on our assembly part using coils that wrap around and heat up to...
Replies
13
Views
3,717
Back
Top Bottom