Formula

siggibald

Member
Join Date
Oct 2012
Location
iceland
Posts
60
hi

how do you write this formula
Dew%20Point.JPG
in the Expressions in CPT --- rslogix 500
 
Just saying

Since everything inside the curly braces is identical, solve for this quantity once and use the result in both numerator and denominator. This will save processing time.
 
Using Doug's idea, it would look like the attached rungs (assuming you have a PLC with the LN function, such as the SLC 5/03 with OS302 or higher, 5/04, 5/05, or ML 1400).

Dew Point.jpg
 
Last edited:
another just saying

I don't know if it's me or what, but I had some trouble already with CPT. I don't think (2+2) is the same thing as ( 2 + 2 ) ... it seems like it wants the spaces. It won't allow you to pick the existing tags... you have to type everything out... I think I'd sooner just use a couple math instructions
 

Similar Topics

Does anybody have a Scaler Formula they would share? Thanks
Replies
11
Views
4,374
Hello all, I'm stuck on some code I want to write. The idea is to have a formula that accepts a DINT tag setpoint, compares it to the previous...
Replies
6
Views
2,436
Hi All, It probably has been discussed before....but... My PLC is a AB L71 Processor (RSLogix5000 v20) I have a Horizontal Round Cylinder Tank...
Replies
27
Views
11,246
Based on your components, how do you calculate what size air conditioner you need for your control panel?
Replies
6
Views
2,341
hi guys, is there any formula to calculate input maximum value in SCP block where input minmum value is -25383 on 0Kg what will the maximum...
Replies
1
Views
1,630
Back