Invertec Optidrive E fault

david.h

Member
Join Date
Mar 2015
Location
Angas Plains
Posts
2
Hello all, I have an old stock new optidrive E that was connected to a .75 kw motor, worked once then now goes direct to a 0-I fault (over current) it does this even with no motor connected. Tried resetting parameters, managed to get it to start and ramp up once (no load conected) now only straight to 0-I. Any thoughts thanks.
 
Sounds very much like a faulty drive. I've used a lot of optidrives and never had one trip with or without a motor, unless there was a genuine fault. If you've performed a factory reset and it still won't go, I'd take it in to your local Invertek rep and ask them to have a look at it. They're usually very helpful, and will probably swap it straight over for a new one if they think it's faulty out of the box.
 
Thanks, any idea who the rep is in South Australia? This unit was purchased online from the US together with some others that are all fine.
 
Hmm, nope sorry no idea about SA. Try google? Although if you bought them from the US he'll probably be somewhat less inclined to help. He certainly won't replace it for you. But if you ask nicely he might at least put it on the bench and confirm it's faulty so you can send it back.
 

Similar Topics

Hi I have a s7-1500 with an invertek drive on profinet the drive runs O.k on profinet but IO only has 4 words in and out all fixed I need to be...
Replies
0
Views
922
Are there any documents that describe how to read/write (control) Invertek VFDs via Ethernet/IP from a ControlLogix PLC? If there are AOP (add-on...
Replies
2
Views
2,301
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
87
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
Replies
2
Views
144
Hi, Experts: We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has...
Replies
7
Views
198
Back
Top Bottom