clear GE FAUNC PLC series 90-30 fault

mike3475

Member
Join Date
Feb 2013
Location
brooklyn ,NY
Posts
334
Hi, Experts:
We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has lost a card". we don't have software (logicmaster 90) for it, how to clear PLC fault table?
Thanks!
 
Last edited:
Loss of an I/O module is not generally a fatal fault, so there may be something else going on. What is your HMI? I think some versions of GE's Cimplicity HMI software included the ability to clear the fault table.
Also, if your CPU is a model that includes a keyswitch and it has been programmed for run/stop you may be able use that to restart as long as the fault isn't fatal.
Other than that, you will need the programming software to clear the fault table. And anyway, the entry in the fault table is your first line of troubleshooting what caused it stop in the first place.
 
Loss of an I/O module is not generally a fatal fault, so there may be something else going on. What is your HMI? I think some versions of GE's Cimplicity HMI software included the ability to clear the fault table.
Also, if your CPU is a model that includes a keyswitch and it has been programmed for run/stop you may be able use that to restart as long as the fault isn't fatal.
Other than that, you will need the programming software to clear the fault table. And anyway, the entry in the fault table is your first line of troubleshooting what caused it stop in the first place.
We have one output card where the top latch was broken , so we use the stick tape to hold it, maybe it got loose and cause output card losing communication, we tried key switch,it can't clear the fault and hmi has no place to clear this fault. I really need is logicmaster 90 software to clear this fault.
Thanks your input.
 
Last edited:

Similar Topics

Hi everyone, recently i worked with a cmore panel and have the question that how can clear alarm list whit remote form,right now only can with...
Replies
0
Views
112
Hi guys, I have a data table as REAL type VALUES_TABLE[32,100]. I want to clear this table. For that i created a REAL type CLEAR_DATA tag with...
Replies
8
Views
565
Hi, I have bought a used 1756-L73S and SP, it is running firmware 30.013 and safety locked, im running Logix Designer 30.01.00. The controller...
Replies
10
Views
1,670
First time using a panelview. I have all of my alarms mapped to bits of dints. How do I get the alarm panel to popup when an alarm happens...
Replies
6
Views
2,128
So I am new to the plc scene, and I am working on a machine that gets a fault, to which I think it is a overtorque fault. I did some research on...
Replies
7
Views
1,978
Back
Top Bottom