Urgent - issue loading Horner OCS program from programmable media

rguimond

Lifetime Supporting Member
Join Date
Jul 2009
Location
Escuminac
Posts
666
A factory technician sent a new program that I loaded onto removable media. The problem is that one of the pressure settings that can't be adjusted from the HMI is wrong. i can change in CScape software and load to removable media, but the HMI says the comm port is locked when I try to reload with the new program!

Any way around this?
 
If you have the program, make the changes through the editor, compile and save.
Then use the menu to create a program that is loadable via the SD card.
Once you create it, copy it to the SD card and follow the same steps to re-load the new program.
(The program generated to be loaded via an SD card cannot be edited, it is I guess just compiled code).
 

Similar Topics

Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
Replies
10
Views
379
I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
Replies
2
Views
230
I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
Replies
9
Views
1,668
Hi all, We are facing synching issues with redundancy module, where the Primary is ending up with disqualified secondary. Normally this would...
Replies
2
Views
625
I have the logic of OMRON but I want to do this logic in TIA 15.1 CPU 1200...
Replies
4
Views
1,836
Back
Top Bottom