i have problem other then PLC,,and hope some can help me,, my ABB inverter ACS510(vfd) work fine on no load or just connecting motor with no load on it,,

on applying rated load to motor inverter work fine unless power intrruption accurs,,on restarting inverter its shows no error but motor do not run,,

i have checked all SMD's and other components and its look fine, can anyone help what kind of fault is it,,


thanks in advance.,,
 
I assume the start command is via terminals (i.e. start pushbutton or relay contact). Some drives can be configured for these inputs to be triggered on level (i.e. if it's on, the drive runs) or transition (input must go from off to on for the drive to run). I don't know the ABB drives at all though so this might be a shot in the dark.

You can test this easily by removing the run signal and reapplying. If the drive then starts then that's the issue.

If it is indeed a safety interlock done via terminals, then you can easily check to see if you have control voltage on the safety input. If not, reset the safety interlock as jraef said
 
Not directly familiar with the ACS535 but, generally, ABB provides a selection of start configurations including one which will not start on powerup with recycling the start signal. This is often the default configuration so you will need to go to the Start/Stop Group (this used to be Group 21 but may be different on the newest models) and select the mode that gives you the restart you want. You do have an Instruction Manual, don't you? If not, it can be downloaded from ABB's website.
 

Similar Topics

Is it possible to connect a PC to the mini console's RJ12 connector? use an RJ12/DB9 cable?
Replies
1
Views
1,002
We purchased a used Radwell ACS 600 "ACS601-0011-4-000B1200801" hoping we could just upload/download parameters from an identical drive or at...
Replies
4
Views
718
Hi all, I have an ABB ACS 600 drive which I am having issues with. The motor runs a platform down to a position then indexes back up to the...
Replies
5
Views
2,177
Hi ,, Could you please any one help me, How to run abb acs 800 drive as encoder less mode by setting parameters on parameter screen.