I am tasked with wiring an analogue output from a Allen Bradley 1771 OFE2 analogue card, to a ABB ACS580 inverter. I'll write a PID loop in PLC5 and send a 4-20mA signal for the inverter frequency.
My question is, how is this exactly ired? I have the diagrams for both pieces of equipment, but i'm not entirely sure.
Please see how i think that it should be done.
Thank you in advance for any help
Nathan
Capture - 1771 OFE2 to acs 580 wiring.PNG Capture - 1771 OF2.PNG Capture - ACS 580 wiring.PNG
The wiring is much simpler than you are attempting to make it.
A -> 2
B -> 3
However, the drive specifies a 0-10 VDC analog signal and the 1771 OFE2 is a 4-20 mA output module.
Hi Bit_Bucket
Thank you for the reply.
It certainly is simpler.
You can alter whether the AI on the inverter is mA or V via parameter 12.15.
I'm assuming its just altering this parameter
Nathan
Hi Bit_Bucket
Nathan
The OFE2 analog output module gets it's loop excitation voltage from the backplane, so there is no need for an external power supply.
I swapped out a 1771 ofe1 with a 1771 ofe2/b. Got the config in and the btw/btr rslogix created. I am having an issue with the scaling registers...
2,094
Hey there, I have a SLC5/05 in a 13 slot rack with a 1747-SN RIO Scanner. The scanner is connected to a PLC5 remote rack. I have to put a...
1,744
Hi everybody, I am installing a new module 1771-OFE2/B to control analog outputs, I know about the BTR and BTW, and I think that all is correctly...
3,356
I have a 1771-OFE analog output card that is controlling a VFD and a modulating gas valve on an AMU. The OFE-2 is in a remote rack that uses a...
3,014
I was called in this morning (too dang early) to help troubleshoot a problem with some newly installed VFD's. We found that the 4-20mA signal was...
7,065