1771 ofe2/b , plc5/20e
bigLee
Jun 2018
Florida
77
I swapped out a 1771 ofe1 with a 1771 ofe2/b. Got the config in and the btw/btr rslogix created.
I am having an issue with the scaling registers. 4095 max keeps pushing 16533 to the data file registers of the btw. Conversely, if I change the value in the data file to 16533 it pushes 1655 to the max scale of that channel in the i/o config.
Any idea where/how this is happening? It is set for BCD data type. I tried two's complement binary option without much change.
This is what I believe to be causing my issues with output current not stepping in a linear fashion. I have to be around half of the scale to get 20mA to drop. It seems a little better on low end but still doesn't oscillate with changing values in btw data file registers.
Ladder 2 rungs 255/256 in attachment.
Any ideas/insight would be appreciated.
Thanks!,
Ben
First, change it from BCD to 2's compliment, otherwise you are going to get confused by what you are seeing in the data tables.
You will see that value that you thought was around 50% is really double the max output.
short on time ...
regarding THIS part of your confusion:
go to the data table and change the Radix setting (lower right corner) to HEX/BCD ... notice that in that format, the 16533 entries are now shown as 4095 ...
here's why in BASIC terms ...
WAY BACK when that module was designed, HEX/BCD was the numerical "format of choice" ... now the setting for Two's compliment (Decimal) is more common ... so what WE usually see in the data table is 16533 - but the same bit pattern appears as 4095 when it gets sent over to the module ...
haven't had time to look at your program code yet ... retirement takes up a lot more time than you'd think ...
Also, just so I'm clear, per the manual there are no jumpers or dip switches to be moved onf 1771 ofe2/b? Maybe just the fault jumper(mid-high-low)?
Since you changed to 2' complement, the need for TOD and FRD went away, if you go online and look at your data table.
Write a CPT for the scaling: Let's use N7:0 as the desired setpoint (0-100). Use limits in your HMI to ensure the max is not above 100.
(N7:0 /100)* 4095, destination N226:3
Thanks for the suggestions! I think I'll try the writing of 100 straight to the card with changed scaling.
As always, much appreciated Ron and Ken!!
If you were using a floating point as your setpoint, I would not recommend the scaling change. But since you are using an integer as your setpoint, you don't need the added resolution.
I was called in this morning (too dang early) to help troubleshoot a problem with some newly installed VFD's. We found that the 4-20mA signal was...
7,063
Hello I am predominantly SIEMENS based, but can use Allen Bradley. I am tasked with wiring an analogue output from a Allen Bradley 1771 OFE2...
1,787
Hey there, I have a SLC5/05 in a 13 slot rack with a 1747-SN RIO Scanner. The scanner is connected to a PLC5 remote rack. I have to put a...
1,741
Hi everybody, I am installing a new module 1771-OFE2/B to control analog outputs, I know about the BTR and BTW, and I think that all is correctly...
3,354
I have a 1771-OFE analog output card that is controlling a VFD and a modulating gas valve on an AMU. The OFE-2 is in a remote rack that uses a...
3,010