ian.smith7
Member
Hi all
I recently worked on an inverter fed 6pole 1.1kw 900rpm 50hz 240v 1.9A motor drivig a roller via a gearbox with a 60/1 ratio. The inverter output was limited to 100hz and the motor seemed to drive ok at that frequency.
The roller was not reaching the required linear speed of 7M/min so I lifted the frequency limit to 125hz as a temporary 'fix' while some new chain drive sprockets were ordered correct the drive ratio.
However when the frequency fed to the motor reached about 115 hz the motor would slow down even though the frequency of the inverter output remained at 115hz. the only load was the gearbox and drive to the roller.
At first I thought the motor had run out of torque so far above the base frequency but the current reading was less than 1 amp ( I did not check the voltage). Then I wondered if it had something to do with it being a 6pole motor? I have seen similar sized 4 pole motors run at higher frequencies.
thanks for any enlightenment,
ian
I recently worked on an inverter fed 6pole 1.1kw 900rpm 50hz 240v 1.9A motor drivig a roller via a gearbox with a 60/1 ratio. The inverter output was limited to 100hz and the motor seemed to drive ok at that frequency.
The roller was not reaching the required linear speed of 7M/min so I lifted the frequency limit to 125hz as a temporary 'fix' while some new chain drive sprockets were ordered correct the drive ratio.
However when the frequency fed to the motor reached about 115 hz the motor would slow down even though the frequency of the inverter output remained at 115hz. the only load was the gearbox and drive to the roller.
At first I thought the motor had run out of torque so far above the base frequency but the current reading was less than 1 amp ( I did not check the voltage). Then I wondered if it had something to do with it being a 6pole motor? I have seen similar sized 4 pole motors run at higher frequencies.
thanks for any enlightenment,
ian