Dear
'm a reseller and have a PO for this Item
And I want to know what's the Difference between Series C and D for this Model ?
:oops:

Ahmed Shaalan
 
1756-EN2T Modules Digitally-signed Firmware Digitally-signed firmware provides additional security over the unsigned firmware. This firmware is different based on the EtherNet/IP modules you use.
• 1756-EN2T/D modules - Support only firmware revision 10.007 in this
enhanced redundancy system bundle. This firmware revision is
digitally-signed.
• 1756-EN2T/C (or earlier) modules - Support only firmware revision
2.007 in this enhanced redundancy system bundle. This firmware revision
is unsigned.

http://literature.rockwellautomation.com/idc/groups/literature/documents/rn/1756-rn650_-en-e.pdf

Regards,
 

Similar Topics

So I have code to read the IP address of a 1756-EN2T with a MSG block - Get Single Attribute. Does anyone know where to find the MSG block...
Replies
12
Views
1,142
I've been trying to get this Ethernet module configured to send emails to our relay server but cannot get it to work. the EN2T is running...
Replies
7
Views
1,762
Dear All, I have been using 5561 CPU with redundancy, Few days ago, I have seen the message Disqualified on RM module of secondary PLC. and i can...
Replies
1
Views
767
Good day folks, We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only -...
Replies
2
Views
2,138
I have a pair of 1756-L73 controllers on A4/A backplanes with PA72 power supplies, configured for redundant operation with RM2 and EN2T modules...
Replies
1
Views
2,782
Back
Top Bottom