I have a pair of 1756-L73 controllers on A4/A backplanes with PA72 power supplies, configured for redundant operation with RM2 and EN2T modules. I noticed that rack #1 was operating as primary with no secondary and rack #2 was disqualified.
The EN2T module on rack #2 had an error message: "Cycle Power to Unit: Assert in File DummyFaultListener.cpp Line 169"
I cycled power, and got a Red OK light and nothing else on the EN2T.
The plant was offline, so I pulled the EN2Ts from both rack and put the one from #1 into rack #2. When I powered rack #2 back on, this EN2T had a different message: "Cycle Power to Unit: Assert in File ../../../Platform/NetLinxUCS/BSP/ICE2/vxbRaGemEnd.c Line 2884"
I put it back in the rack #1 and got a Red OK light, and... nothing else.
I grabbed a spare EN2T and put it in rack #1, it powered up normally and the rack went back to primary with no secondary. But now I've got two bricked EN2Ts and what I suspect is an issue with the backplane of rack #2.
I've reached out to RA support and am waiting for them to investigate, but in the meantime, I was wondering if anyone here has seen anything like this before or has some troubleshooting tips.
..."Cycle Power to Unit: Assert in File DummyFaultListener.cpp Line 169"
Assertions that ask "Have you tried turning it off and on again?"
ROTFL
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
146
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
493
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
127
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
170