I will most certainly have to clarify this in more detail, but here goes.

Talking modbus at 19.2k to 6 Altivar 312 vfds and 2 Altivar 212 drives, currently.

Problem:
Need to add more reads and writes, but don't want to affect the critical writes during machine motion.

Want:
Someone to write a function using the read_var and write_var in Unity that allows me to give certain writes/reads different priority, loops through others, allows me to put an enable bit on the data I want read/written.
 
As usual, first question, what PLC, I presume Schneider and i presume M340 or Premium ?

How do you intend somebody write a program that let's you write when and where you want but not interrupt the comms already going on ?

Either you need to drop your new read_var and write_vars into the existing comms cycles then enable when you need them to be used or stop the critical writes happening so you can write your non critical ones ?

Either way it shouldn't be too hard to do with a little thought and planning.
 
I could do it, but it would take me a long time.
I've been writing plc code for 18 years, but maybe I'm getting old and stupid.
 
yup, M340.
"shouldn't be too hard"
how much ?

Impossible to say without seeing the existing code. Do you need to keep the PLC running while the change is made or is there some downtime to get it in and test it ?

If all the drives are same family it may be better to go Ethernet on the drives and add an NOE card on the M340 then just I/O scan them.
 
would love to go Ethernet. And we are already using an NOE card. Problem, is the ethernet add on to the ATV312 costs more than the drive.
Looking to write a user defined function block for future versions. (aka no reason I can't download the entire program as an update).

The DFB would do reads and writes in a loop, but then would insert the registers to read and write on a priority and enabled input preference.
 
critical

Critical would be the estops.
just kidding
I would like the speed command changes to take priority over lets say, reading drive status.
 
I take it you have some criterion for when the machine is in a critical state or not. Write the extra stuff and slot it in between the criticals whenever the machine is safe, disable when it's moving.

If there's a lot, use a counter and comparators to stagger them, one for each scan or other period of your choice.
 
pretty easy... just look for change in states (on your critical messages) then stop the loop. and perform the writes. I usually always do a constant loop for the reads and interrupt it when I have a write.
 

Similar Topics

Hi everyone, I hope you're all doing well. I'm currently working on updating an HMI project for the GP2500, and I've encountered a bit of a...
Replies
1
Views
92
I've gotten to the learning curve where I can program a call for pump to come on at set point but I'm not sure how to turn the same pump off when...
Replies
1
Views
130
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
Replies
4
Views
159
Thank you for any and all responses/help. I have an RSLogix 5000 v20 and a Cognex In-Sight v5.9 spreadsheet (8502P). I can not figure out how to...
Replies
0
Views
128
Hello, This is my first exposure to CCW Micro8xx family. Someone will write to my existing micro850. Modbus TCP is turned on and I created a...
Replies
2
Views
173
Back
Top Bottom