1734-ADN with IB8/OB8 to 1756-DNB
Hi everybody,
I have with me the following: 1. 1756-L73S controller + 55L7SP safety partner 2. 1756-ENBT 3. 1756-DNB 3a. 1791DS-IB8XOB8 3b. 1734-ADN 3b.i. 1734-IB8 I want to be able create tags for the 1734-IB8 and 1734-OB8 I/O modules so I can program the buttons that are wired in our circuit to these. I've gotten as far as to get steady green LED's on all my modules but only see Local:3:S/I/O and the I/O from the CompactBlock module.3.b.ii. 1734-OB8 What do I need to do? These are the steps I've already taken: - I've added Modules 1~3a to my I/O config in RSLogix5000. - I've created a .dnt for the Subnet called "ADN Network.dnt". - I've created a .dnt for the DeviceNetin "1756-DNB Network". - I've clicked on the 1734-ADN module properties and associated the module with "ADN Network.dnt" - I've then gone into RSLogix5000 and given the path for "ADN Network.dnt" as the DeviceNet file for the 1756-DNB module to link it to the ADN + its I/O. Thanks and best regards. PPW |
You had to give the Adapter module a name, that identifies the rack, then it is just type, slot, channel.
Code:
MyRack:I:Data[2].0 for Input bit 0 on the input card in slot 2, |
Quote:
I'm grateful. :nodi: |