Quote:
Originally Posted by ASF View Post
Welcome to the forum!

To use a third-party controller with a Panelview Plus, you need to use the included Kepware OPC server.

You will need to flash the firmware on the HMI, and when you do, select the relevant Kepware drivers to be loaded onto the hardware. Then you'll need to configure the tags in Kepware to be used in FTView Studio.

That's the short version - now that you know what to look for, give it a try and let us know if you need more help!
Thanks.
I thought about it, but in the firmware for HMI there are no drivers for the Honeywell C200 controller and Kepware Enterprise also does not contain the necessary drivers. The problem is that this equipment is not supported and how this can be changed is not clear.