Loop Consequences
Narlin
Mar 2010
phoenix
320
I want to use a goto Loop in a pH subroutine (RSLogix).
Issue #1: From reading the posts here I have one immediate concern, which is that the watchdog timer S2:3/H will interfere with my loop. I anticipate that the loop needs to be active for ~10 minutes and the watchdog timer defaults to 10ms.
(10 min / 10ms) = 60000!
I rather doubt that i can increase the watchdog timer value enough.
Issue #2: I went into LogixPro Simulator to see what the consequence might be to an infinite loop. To my surprise, it was necessary to use Windows Task Manager to recover. If i manage to put a ML-1100 into such a loop, and since it reboots by running whatever program is loaded, how might I recover. I would like to know this answer before i do the loop!
Narlin
Is there any reason you need to use a loop in your subroutine? I'll admit, I haven't done very "complex" programs, but Jumps and Loops are one thing I've never used in a ladder program. Just always seems that anything I can think of that could use one has a simpler solution that works with the way a PLC ladder program is executed.
Especially considering you want to "stay in the subroutine" for 10 minutes. Seems like you are trying to use a programming language thought process (like C++) when programming ladder logic.
I agree with Tharon. LAD2 is already an infinite loop, just count passes through it...
Narlin
It will fault (and stop the running program) when the watchdog timer is done, killing all outputs and just sit there with a red light saying "fix me". If you power cycle it or otherwise clear faults and put it in run mode, it will do the same thing again. I am not sure what the max watchdog timer is, but that would be that maximum time that your Micro will be "frozen" by the loop. During that period, I don't think you will be able to communicate with it.
Hopefully we have talked you out of using JMP/LBL looping for this task.
Tharon, you are right on my wavelength here. Understanding that the PLC loops continuously and all the time anyway, I am working hard to not use a JMP-LBL loop. I am an old C++ programmer (learned on Fortran), and PLCs can be programmed like that, but i agree that there is also another way.
Any comment on the consequence of an infinite loop?
Describe what you want to accomplish in this 10 minute loop and people here could help you implement it without using loops in ladder.
Without more information there is no way to discuss the merits of an infinite loop within a subroutine. Why do you feel that the normal looping of the PLC is insufficient for your needs? Can you describe your operation?
If in the subroutine continously then the system cannot perform the other functions like communication processing.
The watchdog timer of your ML1100 cannot be made greater than 2.5 seconds, at which time your processor will fault. If you clear the fault and put it in run mode again it will fault again in 2.5 seconds. So in practice you cannot make an infinite loop using JMP-LBL pairs.
For next loops are useful for things you want to process in a single scan - for example you might use one to sum a finite series of values. Otherwise construct your ladder to take advantage of the fact that ladder 2 repeats infinitely.
Thank you for the watchdog timer limit. I see why the jmp-lbl structure exists and that i was thinking about it in a manner not suitable to the PLC device.
Bernie, I am not going to put the logic forward just yet. Part of the fun with these toys is to program them myself. If i get stuck, I will come back for help and give a lot of detail.
I suspect that i am on the right track now.
narlin
Hi, I'm quite new to Rockwell PLC and currently trying to implement the following if Sw1 then for i:=1 to 20 by 1 do xEnable := 1...
369
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
274
I have always controlled servos in Rockwell motion using position loop. I have an application where one process will push against a servo...
271
Hello All Could we get some expertise on flow control ? -Using a PID loop in Productivity 2000 with an analog output, How can we convert...
19
1,588
Complete noob here, using a Click C0-02DD1-D to run a test stand. Requirement is to turn on motor run for X seconds, turn off and dwell for X...
1,083
