Question on AB 1762–IF4 Analog input module saturated
jay mason
Oct 2013
Easton Pa
Trying to figure out why I see 40ma when reading the current inline with the analog card.
I have a load cell with a 4 to 20ma signal and the signal conditioner is set up to split the signal as the force is cycled between compression and tension the zero should be 12.0ma and I read 13 ma at zero and when I press the shunt cal on the signal conditioner I should see 19 ma I get 40ma on the meter and 32768 counts on the plc.
I replaced the 1762–IF4 and I still see the same thing.
Any ideas as to what I am missing?
Thank you
Jay Mason
The IF4 is an input device. It won't generate a current. You have two independent devices that would appear to be indicating your actual current is in excess of 20mA. I would look at your signal conditioner.
Keith
Hey all, Been working on a little project using a Micrologic 1100, Just added this 2-in/2-out analog module (1762-If3Of2)to my project, and a...
2,191
Greetings! In the attached wiring diagram the pairs: DC COM 1, DC COM 2, etc... Are they internally jumpered? So in other words, if I want to...
1,752
Hi All, I have a question about the 1762 if2of2 analog module.When i connect both inputs with voltage option (dip switch on voltage position) i...
2,534
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
169
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
71