Proper landing of shielded wire within cabinet
Search for "cable dismantling tool".
These tools are mainly for stripping the end of cables. To take out a section in the middle, you have to make 2 circular cuts, and then a slit from one circular cut to the other.
shield grounds on the rack right at the I/O modules on one PAC I work on:
Thanks, I thought so, but still left a very small chance that there's some kind of special tool that can make a cut like that :)
Ah, it just so happens that I have a new task where I need to fit everything into a relatively small cabinet.
So I am after having a DIN rail at the bottom of the cabinet, and use this DIN rail for a few teminals, but also for fixing cables and for terminating sheilds on shielded cables.
So what I am after is a shield clamp that fits on a tophat DIN rail.
I have found some, but they all only use spring tension to hold the cable and connect the shield. I really want to use a screw to tighten the clamp real good onto the shield.
In short, a screw-tightened shield clamp for mounting on a 35 mm DIN-rail.
Anyone know such a thing, and preferably from one of the bigger brands ?
so going along with my shielding question i have run into a problem and hope some of the people more experienced then I in this thread will chime in. i will try and keep it to the point.
4-20ma signal from a linear transducer. solid signal when idle, once a VFD turns on in the machine the signal is still steady, just inaccurate. the transducer measures distance traveled of an object and while that object is moving if you watch the PLC its about 2 inches off from real world. by that i mean when i let off the HMI button and the object stops traveling, the number on the screen that was just say 52 is now 54, and if im shooting to stop at 50 with a window of + or - an inch in the PLC code, you can see the issue. i do not own an oscilloscope.
the transducer has a 4 wire shielded cable run to it, only 3 wires are utilized, 24vdc +, 4-20ma output signal, ground. the three wires go to a junction box on the machine and are all landed on pass through terminal blocks. inside the cabinet the the ground and the shield are landed on a pass through terminal block right near the analog input card, the other side of the terminal block goes directly to the grounding lug within the cabinet. The transducer is mounted on a solid piece of metal within the machine, BUT between the transducer body and the metal there is a piece of plastic because it was thought by someone else that it would "help with the noise". The bolts used to mount said transducer to the metal plate are also plastic.
where should i start to attempt to solve my issue? i believe my first order of business should be to get rid of that plastic thats in there because from what i can read, at least from a different manufacturer, the transducer body itself should be grounded. any and all advice welcome.
Sounds to me like you're getting EMF from a variable speed drive. That could be because your transducer (or transducer wiring) is too close to the motor or the cable feeding the motor. I've even seen noise introduced into the AC control power from drives without input reactors or an isolation transformer affect analog inputs. Is your instrument cable run inside a steel conduit? A shield can only reject so much noise.
Dear All Please help me about Below picture problem.PLC not communicating proper.
193
Hi. I’m looking to replace a basic Shark power monitor with a newer one with communication options, probably PowerMonitor 5000. The existing one...
1,010
hello guys, i<m wondering if any body knew a method to export a routine with its proper tags in rslogix studio please
2,597
This may be a dumb question, but do you try to nail the VFD size on the head or go up a size? I can see the value in going up a size of VFD in...
4,819
We've had an intermittent issue with this for years. The application is sensing a level, or more accurately the absence of level in smallish ~5-10...
7,500