E&H Proline Promass 300 Ethernet/IP - totalizer resets
phuz
Jun 2008
Mohnton, PA
1,044
Does anyone have any insights on how to use these meters with Ethernet/IP? The values on the input table look fine, but I can't figure out how to reset the totalizers in the code. The manual shows setting a value to the Control_Totalizer_1 word to "32490" will Reset & Stop, but it has no effect.
I tried calling E&H and I don't believe the workers in tech support have any idea how this works. I was sent a word document explaining how to reset the totalizers from the meter's head. šŸ™ƒ
Sorry I'm late
In case anyone is still wondering...
Set the value of <Meter_Name>:O1.Totalizer_1_Control_Totalizer_1 to the desired action listed in the manual. Once set, you need to toggle <Meter_Name>:O1.TIC_Control_1_Activation to run the command.
Thanks for the update. Explanations of Task-based functions are valuable to the 'community'.
I just tried this and it worked.
value of "-32490" in FlowMeter:O1.Totalizer_1_Control_Totalizer_1
As soon as FlowMeter:O1.TIC_Control_1_Activation went high the totalizer cleared but it also stopped the totalizer. You also have to set FlowMeter:O1.Totalizer_1_Control_Totalizer_1 to 0 before sending the same command again.
Another solution is to send "198" - Reset and Add.
The steps would be:
FlowMeter:O1.Totalizer_1_Control_Totalizer_1 = 198
FlowMeter:O1.TIC_Control_1_Activation = 1
(totalizer clears and starts totalizing from 0 instantly)
FlowMeter:O1.TIC_Control_1_Activation = 0
FlowMeter:O1.Totalizer_1_Control_Totalizer_1 = 0
Or,
After sending "-32490", send "-32226" to start the totalizer back up. This looks to take fewer steps......
hello dear friends. we have bought "proline prowirl 200 vortex flowmeter" but i dont know which connector is for power supply. i have read the...
3,951
How is it going y'all? So We have had a pesky problem with an EH 300 flow meter. We are using EIP to reset the totalizer, and for some reason the...
789
I have a project including S7-300 CPU 314 2PN/DP and this CPU will communicate with Promass 83DP. I tried to connect the flow meter through the...
2,898
Hello All, we have several ethernet IP promass 83 flowmeters from Endress + Hauser in our facility that we use to measure how much material we...
2,391
What is the correct way to reset the totalizator from a allen bradley plc on a promass 100 flow meter. thanks
3,678
