Panelview 1000 updating Floats
Nametag
Mar 2013
Calgary
Hello this is my first post go easy on me please.
I am having an issue with a panelview 1000 (2711-T10G1) i am getting an error "661 Timeout- no block transfer writes" The panelview communicates with the 1747-L532c/d 5/03 CPU through a 1747-sn RIO Scanner. There is also a Wonderware PC/HMI connected to the programming port on the PLC communicating through (DF-1 I think) But The Wonderware updates with no issues. Level is polled by wonderware and a Volume calculation is done and sent back to the plc and then written to the panelview. The #F and #N are COP to #M0 to write to the panelview instead of BTW because BTW is not supported. The #N seem to update on the panelview but the #F do not.
If power is cycled to the panelview or i restart from the system pages the floats will update once but not continuously. If I disconnect the Wonderware PC, the Panelview Will update the last value calculated in Wonderware and I can change the value in rslogix500 data table and it updates on the panelview.
I changed one of the read/write registers in wonderware and then MOV it to the register written to the panelview in case the read/write tags in wonderware was the issue but did not make a difference. Also the operators tell me this problem comes and goes for months at a time....
In the panelview
Comm Setup. RIO
type: slc5/03 os302 1747-sn series b
Rack: 2
Module : 6,7 box is checked
last chassis: checked
baud rate: 230400
block transfer addresses line up
PLC Chan0 - System
DF1- full duplex
Baud: 9600
Parity: none
Stop bits: 1
Source ID: 9
No Handshaking
Error Detection : CRC
Embedded responses : Enabled
Duplicate packet detect is checked
Chan0- User
ASCII
Baud: 9600
Parity: none
Stop bits: 1
data bits : 8
no handshaking
delete mode: ignore
chan1- system
DH485
Baud: 19200
node address: 1
There's probably either a noise problem on the RIO cable, or something wrong with the Block Transfer Write logic in the SLC.
You'd have to post the whole SLC-500 program for an experienced user to have a look if you want to pursue this as a community troubleshooting project.
Do the BTW error message and the "data not updating" issues seem to happen at the same time, or are they separate occurrences ?
The issues are at the same time, the error "pops-up" about every two minutes or so. When the wonderware pc is disconnected the error does not come up and i can enter values in the data viewer and the panelview updates.
I have uploaded the .rss file
I seem to remember that type of error happens when one device is "faster" than the other. Some message bits can be lost. Your Panelview is set at 230400 baud, which is much faster than the PLC.
There can't be a speed mismatch: RIO won't work at all if the devices aren't set for the correct data rate.
The 1747-SN has some diagnostic information in the M1 file that you can copy out of it periodically and examine in controller memory. It's described in the 1747-SN User Manual starting on page 4-23. Of particular interest to you should be the Retry Counters, described on page 4-30.
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
133
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
210
Hi All, I was wondering if it is possible to use parameter files that can be passed to a second page eg: --HOME ---PUMP 1 FACEPLATE (With...
1,135
Hi! I recently discovered how to get to configuration mode and disable printing for connecting to PanelBuilder32 and updating my Panelview...
448
Last night electricians replaced the panelview and now there is no comms between the panelview and the PLC. The processor is a 1747-L541 SLC 5/04...
897