Structured Text Increment Integer
dschmiddr
Nov 2013
Sacramento
If I have an integer and I want it to increment one value every time a condition becomes true then how can I write that logic in structured text. For example
if MachineState = 0 then
DownCount := DownCount + 1;
But when I run this code the DownCount increments by one every scan. I can't get the logic to work. Surely this is a common scenario and I would appreciate anybody's help. Thank you.
I would do it like this using r_trig:
Code:
fbMachineStateR_TRIG(CLK:=bMachineState, Q=>,);
IF fbMachineStateR_TRIG.Q THEN
END_IF
or without r_trig:
Code:
IF NOT bOldMachineState AND bMachineState THEN
END_IF
bOldMachineState:=bMachineState;
On your code it counts all the time when MachineState condition is 0, that means calculation is done everey cycle if that condition is 0
Using one-shot (bool) logic is how I typically approach this:
Code:
if ( MachineState == 0 && !OneShot )
   DownCount = DownCount + 1;
   // other code
OneShot = ( MachineState == 0 );
This example is C++ syntax but you can easily convert it to ST.
Obviously you won't be able to use the same 'OneShot' reliably elsewhere in your code, so you could declare a BOOL array or DINT (using its bits as individual one-shots) to handle multiple state changes, for example.
Increment Integer with Studio 5000 (AB) in ST
Hello,
Everybody's replies have been great. Is there anything to consider if the it is an AB ControlLogix controller. For example the R_TRIG instruction is not available in AB.
Basicly you can do powerfull code with minimal cycle time with ST if compare to ladder or fbd programming.
Ha - the ST/LD debate goes on. Yes ST is good for a lot of things but LD is a lot quicker DEPENDING on the software you are using. Mostly use Omron CX-Programmer and program with the keyboard and just numbers (no I or Q either) and it is really fast. Doing a job with Unity Pro XL at the moment and it is not set up for ladder and the use of numbers at all - only symbols. Lots of ST and taking twice as long as with Omron. That being said a lot of maths are much easier in ST than LD but can still be painful. I do not do motion at this point so have no knowledge of the good and bad there. For an increment @INC D2500 instruction is just so simple it is not funny. I might also add that mapping data to memory areas in Unity Pro for BMS and the like to extract via Modbus TCP is so easy in Unity Pro it is not funny - lots of it to do and just do in Excel and import. Horses for courses. Pluses and minuses everywhere - depends what you are doing.
personally I think that Structured Text is more trouble than it's worth in this situation - but the following ideas might prove useful to you - assuming that you're interesting in something along the lines of the Allen-Bradley "book" way of doing it ...
one way of looking at the "One Shot Rising with Input" instruction - is that the Structured Text syntax is based on the syntax for a Function Block Diagram version - but - with STX you don't get the "picture" of the instruction ...
Hello, doing switch from FBD to ST. First task is converting my old work. How do you sum variables? For example, Interlock1, interlocl2 and...
194
Hello, I am using studio 5000 pro and am trying to figure out the structured text. Here's my scenario: An operator scans a barcode, the barcode...
352
I have an expression in a structured text routine of a Logix controller that looks more or less like the following: ResultInteger := Integer1 *...
441
Good evening. I display the step number of a SFC on a display. Sometimes, on a trip, it goes quickly through many steps and I need to prove to...
185
I am trying to set up a piece of equipment with a Horner HE-X4R. I'd like to use structured text and so far I'm just trying to get a basic On/off...
108
