The Allen Bradley Analog Output module 1762-OF4 with a ML1200 processor, when using old version of RSLogix 500 (5.5) no window comes up to configure the module to 4-20mA from 0-20mA, use to be able to do it through bits, the module is listed as "other-product id 66" in the configuration window, vendor recommends upgrading software, but we are going to buy RSLogix 5000 for another project, is the MicroLogix 1200 programmable with 5000? Our old 500 is version 5.5. Any suggestions??:D
1762-of4
Well, updated the RSLogix 500 and got the config. window, but the module will only allow either -10 to +10V or 4-20 but when you enter in 0 in Engineering units, it should give a 4mA signal, but gives 0 so it seems to work as a 0-20mA not 4-20, in order to get 4mA need to enter around 6500 (0-32767)I am confused...