Can't establish communication
Kaktus33
Feb 2018
Gonduras
Hi. I have a PanelView Plus 600 panel and a Honeywell C200 controller. The task is to connect them for joint work. FTView Studio 6.10 software is installed to work with the panel, but RSLinx Enterprise does not define a Honeywell controller. There is RSLinx Classic for which EDS files for Honeywell equipment are installed. It sees and recognizes the controller. But there is no way to put these EDS files in RSLinx Enterprise. Any ideas how to get out of this situation?
Welcome to the forum!
To use a third-party controller with a Panelview Plus, you need to use the included Kepware OPC server.
You will need to flash the firmware on the HMI, and when you do, select the relevant Kepware drivers to be loaded onto the hardware. Then you'll need to configure the tags in Kepware to be used in FTView Studio.
That's the short version - now that you know what to look for, give it a try and let us know if you need more help!
Thanks.
I thought about it, but in the firmware for HMI there are no drivers for the Honeywell C200 controller and Kepware Enterprise also does not contain the necessary drivers. The problem is that this equipment is not supported and how this can be changed is not clear.
Honeywell C200 controllers share some hardware with Rockwell Automation ControlLogix because of the joint venture for process control applications more than fifteen years ago. Rockwell called it ProcessLogix, Honeywell called it PlantScape.
I don't know if FactoryTalk View (and thus the PanelView Plus 600) will work with any of the Honeywell operating system objects.
I recommend researching support in the C200 controller for Modbus/TCP protocol support. The PV+600 does support Modbus/TCP via the Kepware driver suite.
Thanks, I'll try to work in this direction.
I have Bailey infi 90 DCS system The composer (EWS) was unable to establish communication with ICI . I got this error message anyone has any...
472
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
637
Hi; We have Allen Bradley Power Flex750 inverter drive. I want to establish communication between Laptop and drive for which I have a set of...
1,873
hi guys, i've got a siemens CPU 312-1AE14-0AB0 and when power-up the SF red light turns on. tried to reset the CPU via the MRES switch but still...
1,202
Hi everyone, I need to establish the communication with two differents PLC platforms (Siemens S7 400 and Micrologix 1400) for a project. We...
3,602